Hardware documentation
for CX90x0 Ethernet controller
CX900x-xxxx
CX901x-xxxx
CX90x0-Nxxx
version:2.4
date:2008-06-11
Table of contents
Table of contents
1. Foreword
Notes on the documentation
Safety instructions
4
Documentation issue status
6
2. Product overview
7
Appropiate use
7
System overview
8
Basic modules
9
Technical data
CX900x-0xxx (E-bus)
CX900x-1xxx (K-bus)
CX9010-0xxx (E-bus)
CX9010-1xxx (K-bus)
9
10
11
12
13
Configurations CX9000
14
Configurations CX9010
15
Connections
16
Battery compartment
20
DIP switch settings
21
System interfaces
24
Technical data
24
Connections CX9000-N010
25
Connections CX9000-N030
27
Connections CX9000-N031
28
3. Transport
Unpacking, installation and transport
4. Assembly and connecting
31
31
32
Mechanical assembly
32
Dimensions
32
Mechanical assembly of basic module
35
Mechanical assembly of UPS module
37
Start-up procedure
Start-up procedure
5. Error handling and diagnostics
CPU basic module
40
40
41
41
LED basic module E-Bus
41
LED basic module K-Bus
42
K-Bus diagnosis with TwinCAT
44
6. Decomissioning
Removal and disposal
Embedded PC
46
46
Table of contents
7. Appendix
48
Update image
Accessories
57
Certifications
58
Support and service
2
48
59
Embedded PC
Foreword
1. Foreword
Notes on the Documentation
This description is only intended for the use of trained specialists in control and automation engineering who are
familiar with the applicable national standards. It is essential that the following notes and explanations are followed
when installing and commissioning these components.
Liability Conditions
The responsible staff must ensure that the application or use of the products described satisfy all the requirements for
safety, including all the relevant laws, regulations, guidelines and standards.
The documentation has been prepared with care. The products described are, however, constantly under
development. For that reason the documentation is not in every case checked for consistency with performance data,
standards or other characteristics. None of the statements of this manual represents a guarantee (Garantie) in the
meaning of § 443 BGB of the German Civil Code or a statement about the contractually expected fitness for a
particular purpose in the meaning of § 434 par. 1 sentence 1 BGB. In the event that it contains technical or editorial
errors, we retain the right to make alterations at any time and without warning. No claims for the modification of
products that have already been supplied may be made on the basis of the data, diagrams and descriptions in this
documentation.
© This documentation is copyrighted. Any reproduction or third party use of this publication, whether in whole or in
part, without the written permission of Beckhoff Automation GmbH, is forbidden.
Embedded PC
3
Foreword
Safety Instructions
Safety Rules
State at Delivery
All the components are supplied in particular hardware and software configurations appropriate for the application.
Modifications to hardware or software configurations other than those described in the documentation are not
permitted, and nullify the liability of Beckhoff Automation GmbH.
Personnel Qualification
Description of safety symbols
The following safety symbols are used in this operating manual. They are intended to alert the reader to the
associated safety instructions
Danger
This symbol is intended to highlight risks for the life or health of personnel.
Warning
This symbol is intended to highlight risks for equipment, materials or the environment.
Note
This symbol indicates information that contributes to better understanding.
Operator's obligation to exercise diligence
The operator must ensure that
· the product is only used for its intended purpose.
· the product is only operated in sound condition and in working order.
· the instruction manual is in good condition and complete, and always available for reference at the location where
the products are used.
· the product is operated only by suitably qualified and authorised personnel.
· the personnel is instructed regularly about relevant occupational safety and environmental protection aspects, and is
familiar with the operating manual and in particular the safety notes contained herein.
National regulations depending on the machine type
Depending on the type of machine and plant in which the product is used, national regulations governing the
controllers of such machines will apply, and must be observed by the operator. These regulations cover, amongst
4
Embedded PC
Foreword
other things, the intervals between inspections of the controller. The operator must initiate such inspections in good
time.
Operator requirements
Read the operating instructions
All users of the product must have read the operating instructions for the system they work with.
System know-how
All users must be familiar with all accessible functions of the product.
Embedded PC
5
Foreword
Documentation Issue Status
Version
Changes
2.4
system interfaces CX1200-xxxx removed
2.3
new installation positions are added
2.2
changes in names of system interfaces CX90x0-N070 and CX90x0-N080 inserted
2.1
notes on new system interfaces CX90x0-N070 and CX90x0-N080 added
2.0
notes on UL added
1.9
order information changed
1.8
notes on K-Bus diagnosis added
1.7
notes on USV and CF card handling added title picture changed
1.6
Notes on software image update
1.5
cable length for DVI cable corrected
1.4
consumption value for CX1020-A001 added
1.3
notes on dip switches and image update added
1.2
information for CF-cards changed, errors in product numbers corrected
1.1
notes for system interface N010 added
1.0
revised version
0.0.1
preliminarily version
6
Embedded PC
Product overview
2. Product overview
Appropriate Use
The CX-SYSTEM device series is a modular control system designed for top-hat rail installation. The system is
scalable, so that the required modules can be assembled and installed in the control cabinet or terminal box as
required.
Only switch the PC off after closing the software
Before the Embedded PC is switched off, the software currently running on it should be stopped properly in order to
avoid data loss on the hard disk. Please read the section on “Switching off”.
Switch off all system components and uncouple the Industrial PC from the system if the PC is not used for control
purposes, e.g. during a function test.
System components that have been switched off must be secured against being switched on again.
The power supply unit of the Embedded PC requires a 24 V DC supply.
Danger
Do not exchange any parts when under power!
When components are being fitted or removed, the supply voltage must be switched off.
Software knowledge
Warning
Mandatory software knowledge!
Every user must be familiar with any of the functions of the software installed on the PC that he can reach.
Embedded PC
7
Product overview
System overview
Ethernet-Controller CX9000
With the Ethernet controller CX9000, Beckhoff presents a further extension of the family of CX-type embedded
controllers. The CX9000 is a compact, high-performance yet cost-effective PLC and motion controller for 30 mm DIN
rail mounting. Within the Beckhoff control world it is positioned between the Bus Terminal Controller series BX and
the Embedded PC CX1000. The main feature of this devices is an energy-saving 266 MHz Intel® IXP420 CPU with
XScale® technology that runs under the Microsoft Windows CE operating system. It thus offers adequate computing
capacity even for complex automation tasks. The CX9000 requires no external storage media – the device boots the
operating system from the internal fl ash. Due to the low power consumption, within the specified operating range no
fan is required. The CX9000 therefore requires no rotating components. As usual for the CX series, the device
features a modular mechanical design. In its basic configuration, the compact device only measures 58 x 100 x 91
mm.
EtherCAT as fast I/O-System / K-Bus as alternative I/O-System
The CX9000 is available in two versions: with K-bus for direct connection of Bus Terminals, and as an E-bus version
for direct connection of EtherCAT Terminals. In the basic confi guration, two RJ 45 sockets that are internally
connected to an integrated switch are available as interfaces. This simplifies wiring of several CX9000 within a line
topology. No separate switch hardware is required. The two externally accessible Ethernet ports are independent of
the EtherCAT interface, which is served by a second MAC (media access controller) provided by the CPU.
Basic module and Systeminterfaces
Further interfaces may be added ex works as required: A screen display can be realized using a CX9000-N001
device, i.e. a module combining DVI/ VGA + 2 x USB 2.0. The combination of DVI and USB enables all types of
Beckhoff Control Panel with DVI/USB interface to be used. Touch functionality is connected via USB. As a further
option, two RS232 modules or two RS422/RS485 modules can be configured as COM1 and COM2. All serial
interfaces feature opto-decoupling. Mass storage in form of a Compact Flash card can be used via the CX9000-A000
module, which offers physical storage capacity in the range of several gigabytes.
SPS, Motion Control and Visualization
Like for all Beckhoff controllers, TwinCAT is used for programming the CX9000 as an automation device. The device
itself contains the run-time environment for PLC and Motion Control. One of the two Ethernet interfaces is used as
programming interface.
Software
Microsoft Windows CE enables the creation of fully graphic user programs,which are able to satisfy high
expectationsthanks to the graphics chip integrated in the CX9000.
In summary, the CX9000 is a compact Ethernet controller, which in combination with EtherCAT I/O allows very fast
I/O control cycles. Windows CE and TwinCAT CE constitute the powerful software architecture for this controller.
8
Embedded PC
Product overview
Basic modules
Ethernet-Controller CX90x0
The CX9000 is a compact, top hat rail-mountable Ethernet Controller with direct connection to the Beckhoff I/O
systems in IP 20. The CX90x0 is available in four basic versions: two version for Bus Terminals with K-bus, the other
two for EtherCAT Terminals with E-bus. The CX90x0 comprises the CPU (available in 266 MHz and 533 MHz), the
internal flash memory with two configuration options, the main memory (RAM) (available in two different sizes), and
NOVRAM as non-volatile memory. Two Ethernet RJ 45 interfaces are also part of the basic configuration. These
interfaces are connected to an internal switch and offer a simple option for creating a line topology without the need
for additional Ethernet switches. A memory medium in Compact Flash format I and II is available as an optional
module.(only in combination with system interface CX90x0-N010) The operating system is Microsoft Windows CE.
The TwinCAT automation software transforms a CX90x0 system into powerful PLC and Motion Control system that
can be operated with or without visualization. Further system interfaces can be connected to the CPU module ex
works. The CX9000-N010 option can be connected to Beckhoff Control Panels or standard monitors with DVI or VGA
input via the DVI and USB interfaces. Devices such as printer, scanner, mouse, keyboard, mass storage, CR-RW etc.
can be connected via the USB2.0 interfaces. The module CX90x0-N030 offers two serial RS232 interfaces with a
maximum transfer speed of 115 kbaud. These two interfaces can be implemented as RS422/RS485, in which case
they are identified as CX90x0-N031.
The Ethernet-Controller CX90xx is offered in four versions:
CX900x-0000 E-bus connection
CX900x-1000 K-bus connection
CX9010-0000 E-bus connection
CX9010-1000 K-bus connection
Embedded PC
9
Product overview
Technical data – CX9000-0000 E-bus connection
Technical data
CX9000-0000
Processor
Intel® IXP420 with Xscale® Technology, 266-MHz clock rate
Internal flash memory
16 Mbyte Flash (internal, expandable up to 32 Mbyte)
Internal main memory
64 Mbyte RAM (internal, expandable up to 128 Mbyte)
interfaces
2 x RJ 45 (internal Switch), 10/100 Mbit
Diagnostics LEDs
1 x Power, 2 x LAN, 1 x L/A, 1 x flash access
Clock
internal battery-backed clock for time and date
Operating system
Control software
TwinCAT-CE-PLC-Runtime or TwinCAT-CE-NC-PTP-Runtime
Power supply
24 VDC (-15%/+20%) To meet the UL requirements use a 4 A fuse or a power
supply that has to satisfy NEC class 2!
Dielectric strength
500 Vrms (supply/internal electronics)
I/O connection
E-bus (EtherCAT Terminals)
NOVRAM
128 kByte
I/O-DPRAM
Power supply I/O
terminals
2A
Max. power loss
6 W (including CX9000-xxxx system interfaces)
Dimensions (W x H x D)
59 mm x 100 mm x 91 mm
weight
ca. 250 g
Operating / storage
temperature
0° C ... +50° C / -25° C ... +85° C
Relative humidity
95% no condensation
Vibration/shock
resistance
conforms to EN 60068-2-6 / EN 60068-2-27/29
EMC resistance
burst/ESD
conforms to EN 61000-6-2/EN 61000-6-4
Protection class
IP 20
10
Embedded PC
Product overview
Technical data CX9000-1000 K-bus connection
Technical data
CX9000-1000
Processor
Intel® IXP420 with XScale® Technology, 266-MHz clock rate
16 MByte Flash (internal, expandable up to 32 MByte)
64 MByte RAM (internal, expandable up to 128 MByte)
interfaces
2 x RJ 45 (internal Switch), 10/100 MBit
Diagnostics LEDs
1 x Power, 2 x LAN, 1 x K-Bus, 1 x Flash-Zugriff
Clock
Operating system
Control software
Power supply
Dielectric strength
I/O connection
K-bus (Bus Terminals)
NOVRAM
128 kByte
I/O-DPRAM
4 kByte
Power supply I/O
terminals
2A
Max. power loss
weight
ca. 250 g
Operating / storage
temperature
Relative humidity
95% no condensation
Vibration/shock
resistance
EMC resistance
burst/ESD
Protection class
IP 20
Embedded PC
11
Product overview
Technical data – CX9010-0000 E-bus connection
Technical data
CX9010-0000
Processor
Intel® IXP420 with Xscale® Technology, 533-MHz clock rate
32 Mbyte Flash (internal)
128 Mbyte RAM (internal)
interfaces
Diagnostics LEDs
Clock
Operating system
Control software
Power supply
Dielectric strength
I/O connection
NOVRAM
128 kByte
I/O-DPRAM
Power supply I/O
terminals
2A
Max. power loss
7 W (including CX9000-xxxx system interfaces)
weight
ca. 250 g
Operating / storage
temperature
Relative humidity
95% no condensation
Vibration/shock
resistance
EMC resistance
burst/ESD
Protection class
IP 20
12
Embedded PC
Product overview
Technical data CX9010-1000 K-bus connection
Technical data
CX9010-1000
Processor
Intel® IXP420 with XScale® Technology, 533-MHz clock rate
32 MByte Flash (internal)
128 MByte RAM (internal)
interfaces
Diagnostics LEDs
Clock
Operating system
Control software
Power supply
Dielectric strength
I/O connection
NOVRAM
128 kByte
I/O-DPRAM
4 kByte
Power supply I/O
terminals
2A
Max. power loss
7 W (including CX90x0-xxxx system interfaces)
weight
ca. 250 g
Operating / storage
temperature
Relative humidity
95% no condensation
Vibration/shock
resistance
EMC resistance
burst/ESD
Protection class
IP 20
Embedded PC
13
Product overview
The order identifier of the basic CPU module is derived as follows:
Following CX9000 configurations are available:
Ordering
information
16 MB Flash
64 MB RAM
32 MB Flash
128 MB RAM
EBus
KBus
DVI,
2x
USB
no
TwinCAT
TwinCATPLCRuntime
TwinCATNCRuntime
CX9000-0000
x
CX9000-0001
x
x
CX9000-1000
x
x
CX9000-1001
x
x
CX9001-0000
x
x
x
CX9001-0001
x
x
x
CX9001-0002
x
x
x
x
CX9001-0100
x
x
x
x
CX9001-0101
x
x
x
x
CX9001-0102
x
x
x
x
x
CX9001-1000
x
x
x
CX9001-1001
x
x
x
CX9001-1002
x
x
x
x
CX9001-1100
x
x
x
x
CX9001-1101
x
x
x
x
CX9001-1102
x
x
x
x
x
14
Embedded PC
Product overview
K-Bus
DVI, 2 x
USB
no
TwinCAT
TwinCATPLCRuntime
TwinCATNCRuntime
x
x
CX9010-0001
x
x
CX9010-0002
x
x
x
CX9010-0100
x
x
x
CX9010-0101
x
x
x
CX9010-0102
x
x
x
x
CX9010-1000
x
x
CX9010-1001
x
x
CX9010-1002
x
x
x
CX9010-1100
x
x
x
CX9010-1101
x
x
x
CX9010-1102
x
x
x
x
Ordering
information
E-Bus
CX9010-0000
Embedded PC
15
Product overview
Connections
The system is supplied with power via the integrated power supply. This is wired as follows:
The basic module is powered via the upper connectors with 24 V DC. The terminal bus can be supplied via the lower
connections.
UL requirements
Danger
For the compliance of the UL requirements the CX-Controllers should only be supplied
by a 24 VDC supply voltage, supplied by an isolating source and protected by means of a
fuse (in accordance with UL248), rated maximum 4 Amp.
by a 24 VDC power source, that has to satisfy NEC class 2.
A NEC class 2 power supply shall not be connected in series or parallel with another
(class 2) power source!
These UL requirements are valid for all supply voltages of the CX-Controllers!
16
Embedded PC
Product overview
CPU basic module with 2 Ethernet RJ 45 connectors:
RJ 45 interface (socket):
Assignment of the RJ45-interface, Port 1:
PIN
Signal
Desciption
1
TD +
Transmit +
2
TD -
Transmit -
3
RD +
Receive +
4
connected
not used
6
RD -
Receive -
7
connected
not used
5
8
TD & RD are exchanged at the hubs or between two PCs.
Assignment of the RJ45 interface, Port 2:
PIN
Signal
Description
1
TD +
Transmit +
2
TD -
Transmit -
3
RD +
Receive +
4
connected
not used
6
RD -
Receive -
7
connected
not used
5
8
Connection of the Ethernet ports:
Warning
The two Ethernet ports of a basic CPU module must not be connected to the same external switch!
Note
Only for use in LAN, not for connection to telecommunication circuits.
Schematic structure of the network components:
The CX9000 features two MAC blocks. The first one (MAC1) operates the network interfaces for the Ethernet ports.
The two outputs are connected via a switch. In this way a line structure can be configured as described below. From
an operating system perspective this represents a single connection. The second block (MAC2) operates the
extended PC104 bus. The second physical network connection is used to run the E-bus connection. (in version
CX900x-0xxx) The signals are connected to and FPGA. This unit converts the Ethernet signals to E-bus signals. So
EtherCAT terminals can be connected to the system.
Embedded PC
17
Product overview
If K-bus is used as terminal bus (CX900x-1xxx), the second MAC-interface is not connected.
Operating system perspective:
The operating system only sees one of the connections for the network interface. The status is always connected,
since the switch is connected directly.
18
Embedded PC
Product overview
These interfaces are connected to an internal 3-port switch and offer a simple option for creating a line topology
without the need for additional Ethernet switches.
Basic CPU module with DVI/USB interface:
In addition to the two Ethernet ports, this basic module also features DVI/USB interfaces. The pin assignment of the
basic CPU module with two USB and a DVI-I interface is explained under the associated CX9000-N010 system
interface.
Applicable to all basic CPU modules:
LED
The green power LED (PWR) is on if the basic CPU module is connected correctly to a live power supply unit.
Compact Flash slot
Further information can be found under Compact Flash slot.
Embedded PC
19
Product overview
Battery compartment
The battery compartment is located on the left-hand side of the CPU module, between the two Ethernet ports.
It can be opened with the aid of a screwdriver (proceed carefully in order to avoid damage).
The battery is a CR2032 type from Panasonic
with the following specification:
Battery
type
CR2032
Electrical properties (at 20° C)
Standard charge
Dimensions
nominal voltage
nominal capacity
continuous load
Diameter
Height
Weight
3.0 V
225 mAh
0.20 mA
20.00 mm
3.2 mm
3.1 g
Danger
Replace Battery Part. No. CR2032 manufactured by Sanyo or Panasonic Only.
Use of Another Battery May Present A Risk Of Fire Or Explosion.
WARNING, Battery may explode if mistreated. Do Not Recharge, Disassemble or
Dispose of in fire.
Spare batteries can be ordered from Beckhoff Service.
20
Embedded PC
Product overview
Dip switch settings
General
Warning
In general there is no need to change the dip switch settings. The switches are installed in case of
major faults, to reset the system, provide debug messages, bypass TwinCAT start and update the
image.
Never change a running system !
To get access to the dip switches, you have to open the over of the battery compartment. It is located between the
two ethernet connectors on the front of the CX9000-N000 module. To open the cover proceed as follows:
1.
Power down the CX9000
2.
Open the battery compartment (located between two ethernet ports)
Once the compartment is opened, the four dip switches can be accessed. They are located left of the battery holder.
On normal operation mode all switches are set to OFF. (All switches are down).
To change the settings of a dip switch its is advised to use a screwdriver with a small blade (2.5 mm x 7.5 cm length
and parallel shaft, Beckhoff order number: ZB8700). Use the edge to move the switches with caution!
The switches have four functions:
1.
Reset CX9000-Sytem to defaults
2.
Send debug codes to COM1 (if connected)
3.
Update mode to obtain a new image via PC server (Boot menu via COM1)
4.
Force TwinCAT to start in config mode
The functions are described in detail below:
Embedded PC
21
Product overview
Reset to Factory Settings:
1.
Set dip switch 1 to ON (move switch 1 up).
2.
Connect CX-System to power and boot system. After a complete boot, the registry is regenerated.
3.
Set dip switch 1 back to OFF (switch 1 down) and close cover.
Report debug messages to COM1:
1.
Set dip switch 2 to ON (move switch 2 up).
2.
Connect a serial monitor device (printer or terminal) to COM1 port. The settings for the interface are: 38400
baud, 8 bits , NO parity and 1 stop bit (38400,8,N,1).
3.
Connect CX-System to power and boot system. Debug messages are sent to the monitor device.
4.
After finishing diagnosis power set dip switch 2 back to OFF (switch 2 down) and close cover.
Bootstrap Mode for updates:
The Bootstrap Mode is implemented for image updates. The procedure is more complex so it is described in an own
part of the documentation. Refer to the instruction for the process.
22
Embedded PC
Product overview
Force TwinCAT in " Config Mode " :
For some cases (e.g. errors in boot project) it is necessary to start TwinCAT in Config mode. So the boot project can
be corrected or other settings can be (re)setted.
1.
Set dip switch 4 to ON (move switch 4 up).
2.
3.
Make changes to the PLC
4.
power down the system. Set dip switch 4 back to OFF (switch 4 down) and close cover.
Embedded PC
23
Product overview
System interfaces - technical data
Dimensions:
Like for the other members of the CX family, a number of optional interface modules are available for the basic
CX9000 CPU module that can be installed ex works. The following interfaces are available:
CX9000-N010 DVI / USB Module
CX9000-N030 serial interface for RS323
CX9000-N031 serial interface for RS422 / RS485
The CX9000-N010 option can be connected to Beckhoff Control Panels or standard monitors with DVI or VGA input
via the DVI or USB interfaces.Devices such as printer, scanner, mouse, keyboard, mass storage, CR-RW etc. can be
connected via the USB 2.0 interfaces. The modules CX9000-N030 offers two serial RS232 interfaces with a
maximum transfer speed of 115 kbaud. These interfaces can be implemented in pairs as RS422/RS485, in which
case they are identified as CX9000-N031 respectively. The system interfaces cannot be retrofitted or expanded in
the field. They are supplied ex factory in the specified configuration and cannot be separated from the CPU module.
The system interfaces run through the internal PC104 bus, so that further CX components can be connected. The
power supply of the system interface modules is ensured via the internal PC104 bus.
Technische Daten
CX9000-N010
CX9000-N030
CX9000-N031
Interfaces
1 x DVI +
2 x USB 2.0
1 x COM1+2, RS232
1 x COM3+4, RS232
1 x COM1+2, RS422/RS485
1 x COM3+4,RS422/RS485
Connection type
DVI-I 29-pin socket +
2 USB Ports type A
2 x D-Sub plug 9-pin
Properties
DVI-I interface also
carries out VGA signals
(DVI-A)
max. baud rate
115 kbaud,
can not be used
simultaneously with
N031/N041
max. baud rate 115 kbaud,
can not be used simultaneously
with N030/N040
Power supply
via system bus (Through internal power supply in CX9000 module)
Dimensions
19 mm x 100 mm x 51 mm
Operating
temperature
0 °C ... +55 °C
Storage
temperature
-25 °C ... +85 °C
Relative humidity
95% no condensations
Vibration/Shock
resistance
EMC resistance
burst / ESD
Protection class
IP 20
wight
app. 80 g
24
Embedded PC
Product overview
CX9000-N010 connections
In addition to the two Ethernet interfaces, this module features a DVI-I and two USB interfaces.
Note
The system interface CX9000-N010 can only be used in CX9000 system with large memory
(CX9001-x00x).
DVI-I interface
The DVI-I interface transfers analog and digital data and is suitable for connection to analog graphics cards with 15
pin D-Sub connector and digital graphics cards with DVI-D output. The resolution at the screen or the Beckhoff
Control Panel depends on the distance (maximum 5 m).
The DVI interface uses VGA signals, so that the connection of CRT VGA monitors to the CX-System using a DVI to
VGA adapter is also possible.
This adapter is available as an accessory.
DVI-I socket:
Pin
Assignment
Pin
Assignment
Pin
Assignment
1
TMDS Data 2-
9
TMDS Data 1-
17
TMDS Data 0-
2
TMDS Data 2+
10
TMDS Data 1+
18
TMDS Data 0+
3
TMDS Data 2/4 Shield
11
TMDS Data 1/3 Shield
19
TMDS Data 0/5 Shield
4
not connected
12
not connected
20
not connected
5
not connected
13
not connected
21
not connected
6
DDC Clock
14
+ 5V Power
22
TMDS Clock Shield
7
DDC Data
15
Ground ( +5V, Analog H/V Sync)
23
TMDS Clock +
Embedded PC
25
Product overview
8
Analog Vertical Sync
16
Hot Plug Detect
24
TMDA Clock -
Pin assignment (cross)
Pin
Assignment
C1
Analog Red Video Out
C2
Analog Green Video Out
C3
Analog Blue Video Out
C4
Analog Horizontal Sync
Resolution at the monitor:
Resolution in pixels
Distance of the interface from the monitor
1600 x 1200
5m
1280 x 1024
5m
1024 x 768
5m
800 x 600
5m
640 x 480
5m
USB interface:
The USB socket is a type A socket. The USB interface complies to USB 2.0 specification
Pin
Assignment
Typical assignment
1
VBUS
Red
2
D-
White
3
D+
Green
4
GND
Black
Shell
Shield
Drain Wire
26
Embedded PC
Product overview
CX9000-N030 connections
The CX9000-N030 system interface features two RS232 interfaces, COM1 and COM2 (9 pin Sub-D plug connector).
The maximum baud rate on all channels is 115 kBit. The pin assignment for all interfaces is equal and described
below. The interface parameter can be set in the operating system or in the PLC program.
RS232 COM interface (connector):
Pin assignment COM interface:
PIN
Signal
Type
Description
1
DCD
Signal in
Data Carrier Detected
2
RxD
Signal in
Receive Data
3
TxD
Signal out
Transmit Data
4
DTR
Signal out
Data Terminal Ready
5
GND
Ground
Ground
6
DSR
Signal in
Dataset Ready
7
RTS
Signal out
Request to Send
8
CTS
Signal in
Clear to Send
9
RI
Signal in
Ring Indicator
Note
The system interface CX9000-N30 can only be used instead and not simultaneously with system
interface CX9000-N031.
The system interface CX9000-N31 can only be used instead and not simultaneously with system
interface CX9000-N030.
Embedded PC
27
Product overview
CX9000-N031 connections
The CX9000-N031 system interface features two RS422 / RS 485 interfaces, COM1 and COM2 (9 pin Sub-D plug
connector). The maximum baud rate on all channels is 115 kBit. The pin assignment for all interfaces is equal and
described below. The interface parameter can be set in the operating system or in the PLC program.
PIN
Signal
Type
Description
2
TxD+
Data-Out +
Transmit 422
3
RxD+
Data-In +
Receive 422
5
GND
Ground
Ground
6
VCC
VCC
+5V
7
TxD-
Data-Out -
Transmit 422
8
RxD-
Data-In -
Receive 422
For RS 485 Pin 2 and 3 ( Data +) as well as Pin7 and 8 (Data -) have to be connected..
28
Embedded PC
Product overview
Setting the interface parameter
If the system interface CX9000-N031 resides at the end of the CX9000-system block, it is easy to access the dip
switches. The dip switches for the configuration of the RS485/422 interfaces can be found at the left side of the
module. If you remove the grey cover you can see the switch:
The upper switch sets the parameters for the upper interface, the lower switch sets the parameter for the lower
interface. The system must be powered down, if the settings of the switches are changed! The settings for default
use should be mentioned by ordering the interface module.
Settings DIP switches RS485:
RS485 without Echo, End-Point ( Terminated) DEFAULT setting
DIP
Status
Function
1
off
Echo on
2
on
Echo off
3
on
Auto send on
4
off
Always send on
5
on
Auto receive on
6
off
Always receive on
7
on
Term on
8
on
Term on
RS485 with Echo, End-Point ( Terminated)
DIP
Status
Function
1
on
Echo on
2
off
Echo off
3
on
Auto send on
4
off
Always send on
5
off
Auto receive on
6
on
Always receive on
7
on
Term on
8
on
Term on
Embedded PC
29
Product overview
RS485 without Echo, Drop-Point ( without Termination)
DIP
Status
Function
1
off
Echo on
2
on
Echo off
3
on
Auto send on
4
off
Always send on
5
off
Auto receive on
6
on
Always receive on
7
off
Term on
8
off
Term on
RS485 with Echo, Drop-Point ( without Termination)
DIP
Status
Function
1
on
Echo on
2
off
Echo off
3
on
Auto send on
4
off
Always send on
5
off
Auto receive on
6
on
Always receive on
7
off
Term on
8
off
Term on
Setting DIP-Switches RS422:
RS422 full duplex end point
DIP
Status
Function
1
on
Echo on
2
off
Echo off
3
off
Auto send on
4
on
Always send on
5
off
Auto receive on
6
on
Always receive on
7
on
Term on
8
on
Term on
Note
The system interface CX9000-N31 can only be used instead and not at the same time with system
The system interface CX9000-N30 can only be used instead and not at the same time with system
30
Embedded PC
Transport
3. Transport
The specified storage conditions must be adhered to (see " Technical data " ).
Dimensions and weight of the individual modules:
Dimensions (W x H x D): 19 x 100 x 91 mm (system interface) , 58 x 100 x 91 mm (basic module)
Weight: 80 g (system interface) to 250 g (basic module)
Unpacking
Proceed as follows to unpack the unit:
1. Remove packaging.
2. Do not discard the original packaging. Keep it for future relocation.
3. Check the delivery for completeness by comparing it with your order.
4. Please keep the associated paperwork. It contains important information for handling the unit.
5. Check the contents for visible shipping damage.
6. If you notice any shipping damage or inconsistencies between the contents and your order, you should notify
Beckhoff Service.
Achtung
Danger of damage to the unit!
During transport in cold conditions, or if the unit is subjected to extreme temperature swings, condensation on and
inside the unit must be avoided.
Prior to operation, the unit must be allowed to slowly adjust to room temperature. Should condensation occur, a delay
time of approximately 12 hours must be allowed before the unit is switched on.
Installation
The devices are designed for installation in control cabinets. You will find installation instructions in the chapter
mechanical mounting.
Shipping and relocation
Despite the robust design of the unit, the components are sensitive to strong vibrations and impacts. During
transport, your computer should therefore be protected from excessive mechanical stress. Therefore, please use the
original packaging.
Embedded PC
31
Mechanical assembly
Dimensions
The CX-System product range is characterized by small overall installed size and high modularity. For project
planning purposes, a CPU module, a power supply unit and the associated system interfaces and fieldbus interfaces
have to be provided. The overall width of the application is made up of the individual modules. With a height of 100
mm, the module dimensions exactly match those of the Beckhoff Bus Terminals. Together with the lowered
connector surfaces, this means that it can be used in a standard terminal box with a height of 120 mm.
Warning
To ensure cooling to the device in operation it is important keep the safety distances.
CX9000-xxxx CPU Basic module:
CX90x1-xxxx and CX1010-xxxx CPU Basic module:
32
Embedded PC
CX9000-N0x0 System interfaces:
CX1100-09x0 UPS module:
CX1100-0900
Embedded PC
33
CX1100-0910
CX1100-0920
34
Embedded PC
Mechanical assembly of the basic module
The installation of the modules takes place in three steps:
1. The sequence of the modules
The basic CPU module with system interfaces, which are factory-installed on the left side, is extended with the power
supply unit on the right and with the fieldbus connection (master or slave) left side if available.
2. Engaging on the top-hat rail
On the bottom of the modules, there is a white tension strap, which is connected with a latching mechanism. These
tension straps must be pulled down before attaching to the top-hat rail. This can be done using an ordinary
screwdriver and a slight turn.
Then fix the CX9000 block on the top hat-rail using the latching straps. You should hear a soft click.
Do not force the module or apply
excessive pressure!
Only apply pressure at insensitive points of the housing (edges). Never apply pressure on the display, the buttons or
movable parts of the CX-System.
After successful latching on the top-hat rail the straps should be pushed back to their original position.
Note:
A locking mechanism prevents the individual housings from being pulled off again. Detailed information relating to
disassembly of the CX-SYSTEM configuration from the top-hat rail can be found on page " Removal and disposal " .
Embedded PC
35
Installation position:
Warning
The maximum ambient temperature for CPU modules mounted on a top-hat rail is 55°C. The
orientation in which the device is fitted must be selected in such a way that cooling air can flow
vertically through the ventilation holes. The images show the correct installation position.
Observe minimum clearance!
Mounting must provide a clearance of 30 mm both above and below a CX-System device
combination to ensure adequate ventilation of the base CPU module and the power supply unit.
Correct installation position:
The high-performance CX9000 system generates a significant amount of heat, which is dissipated via a passive
ventilation system. This system requires the unit to be mounted correctly. Ventilation openings are located at the top
and bottom of the housing. The system therefore has to be installed horizontally. This ensures optimum air flow.
Illegal installation positions:
36
Embedded PC
Mechanical installation of the UPS Module
Note
The UPS module for CX9000 is not fully supported by TwinCAT yet.
The UPS module should be connected the described way. To get the power fail signal (pin 3 on UPS)
must be connected to a digital input terminal. In this way the PLC can
access the power fail signal and save the data or shut down the system. The shutdown time can only
be set by the selector on the front side of the UPS (best choice is 0).
In case of shutdown the UPS will restart the system after power fail.
0. Switching off and disconnecting the power supply
Before a CX9000 system can be dismantled, the system should be switched off, and the power supply should be
disconnected.
1. Removing from the top-hat rail:
Before the individual CX9000 modules are disconnected, the whole CX9000 hardware block should be removed from
the top-hat rail. Proceed as follows:
1.1. Release and remove the first Terminal next to the power supply unit on the top-hat rail.
First remove any wiring from power supply unit and then from the first terminal on the top-hat rail next to the power
supply unit. If the wiring is to be reused for another system, it is advisable to make a note of the connections. Then
pull the orange terminal release (see arrow) to release the terminal and pull it out.
1.2. Releasing the CX9000 system
In order to release the CX-block, pull the white straps at the bottom of the module in the direction of the arrows. They
will lock in the extended position. After pulling the terminal release of the power supply unit, the block can be
removed carefully from the top-hat rail.
Embedded PC
37
2 Assembly of the CPU basic module with UPS module
2.1 Assembly the the CX9000 system block
In order to be able to connect the UPS to the basic CX9000 module, the cover of the basic module has to be
removed first. This is achieved by applying slight pressure on the cover. The individual modules are simply plugged
together. The PC104 connector plugs should be handled carefully in order to avoid damage. When correctly
assembled, no significant gap can be seen between the attached housings. If the modules are assembled the cover
can be replaced.
2.2 Engaging on the top-hat rail
Before engaging the system back on the top-hat rail the user should ensure all white tension straps are pulled down.
The user should take care of the space between the terminals and the Embedded PC system. The space for the
removed terminal must be kept to reinstall the terminal.
38
Embedded PC
excessive pressure!
2.3 Connecting the Embedded PC to the terminal bus
By reinstalling the once removed terminal the system is connected to the bus.
Finally the wiring must be reinstalled. The removed terminal is reconnected as before. The power supply is now
connected via the UPS-connectors. (see chapter connections for details)
Embedded PC
39
Start-up procedure
Switching the PC on and off
Switching on
The power supply for the basic CPU module comes from the power supply unit. The basic CPU module starts
automatically when the power supply unit is connected to the mains.
Switching on for the first time
When you switch on the PC for the first time, the pre-installed operating system (optional) will be started.
Switching off
The Embedded PC switches off when the power supply unit is switched off. The control software typically running on
Embedded PCs should be shut down or stopped correctly. A user who may not close software may also not switch
the Embedded PC off, since data can be lost from the hard disk by switching off while software is running.
Once the software has been stopped, the operating system can be shut down. Only then should the power supply be
interrupted.
40
Embedded PC
CPU basic module
LEDs Basic CPU-module (E-Bus)
Display
LED
PWR
Meaning
red
TwinCAT is in STOP mode
green
TwinCAT is in RUN mode
blue
TwinCAT is in CONFIG mode
off
System is offline
LAN 1
LAN Link , (green)
LINK/ACTIVITY for first switched LAN PORT (CX9000_N000)
LAN 2
LAN Link, (green)
LINK/ACTIVITY for second switched LAN PORT (CX9000_N000)
L/A
(Link Activity) flashes in traffic on E-bus.
HDD
Read/Write Compact Flash (red)
Indicates access to the CF card.
Embedded PC
41
LEDs Basic CPU-module (K-Bus)
Display
LED
PWR
Meaning
red
green
blue
off
System is offline
LAN 1
LAN Link , (green)
LAN 2
LAN Link, (green)
K-Bus
flashes in traffic on K-bus / reports errors
K-Bus not active (off)
K-Bus running (flashes green)
K-Bus error (red) see tables below
HDD
The I/O error K-Bus LED blink code
Fast blinking
Start of the error code
First slow sequence
Error code
Second slow sequence
Error code argument
LEDs for K-Bus diagnosis
Error
Error code
code
argument
Persistent,
continuous
blinking
Description
EMC problems
0
1
Code buffer overflow
2
1 pulse
EEPROM checksum error
Unknown data type
Programmed configuration
has an incorrect table entry
Table comparison (Bus
Terminal n)
0
2 pulses
n (n & gt; 0)
3 pulses
0
0
4 pulses
n
5 pulses
n
0
9 pulses
n (n & gt; 0)
42
Remedy
- Check power supply for overvoltage or undervoltage
peaks
- Implement EMC measures
- If a K-Bus error is present, it can be localised by a
restart of the power supply (by switching it off and then
on again)
Revert to the manufacturer’s setting
Insert fewer Bus Terminals. The programmed
configuration has too many entries in the table
Software update required for the power supply
Check programmed configuration for correctness
Incorrect table entry
- No Bus Terminal inserted
- One of the Bus Terminals is defective; halve the
number of Bus Terminals attached and check whether
K-Bus command error
the error is still present with the remaining Bus
Terminals. Repeat until the defective Bus Terminal is
located.
K-Bus data error, break
Check whether the n+1 Bus Terminal is correctly
behind the power supply
connected; replace if necessary.
Check whether the Bus End Terminal 9010 is
Break behind Bus Terminal n
connected.
K-Bus error in register
Exchange the nth bus terminal
communication with Bus
Terminal n
Checksum error in Flash
program
Bus Terminal n is not
Revert to the manufacturer's setting which will clear the
consistent with the
boot project.
configuration that existed
Embedded PC
14 pulses
n
15 pulses
n
16 pulses
n
when the boot project was
created
nth Bus Terminal has the
wrong format
Number of Bus Terminals is
no longer correct
Length of the K-Bus data is
no longer correct
Start the power supply again, and if the error occurs
again then exchange the Bus Terminal.
Start the power supply up again.
Error code argument
The number of pulses indicates the position of the last Bus Terminal before the fault. Passive Bus Terminals, such as
a power feed terminal, are not included in the count.
In the case of some errors, rectification does not cause the power supply to leave the blink sequence. The power
supply can only be restarted by switching its supply voltage off and on again.
Embedded PC
43
Terminal Bus Analysis in PLC-Program
To analyze the terminal bus (K-Bus) the programmer can access the registers described in the architecture. The
access to the PLC-program is realized via TwinCAT. The registers are described in the architecture of the terminal
bus connectors (CX1100-000x.
For analysis four signals / variables are used:
BusState (describes the state of the bus: 0 - & gt; no error, 1 - & gt; bus error)
ErrorCode (same error code as the LED blink code)
ErrorArg (same argument code LED blink code)
Request[0] (output to request error codes / reset bus)
In the PLC program some external variables must be defined:
VAR
k_bus_request AT %QX0.0
: BOOL;
k_bus_err_code AT %IB0
: USINT;
k_bus_err_arg AT %IB1
: USINT;
k_bus_state AT %IB2
: USINT;
END_VAR
In the PLC program the analysis can be done as follows: (this is only pseudo code)
IF k_bus_state = 1
THEN
k_bus_request := TRUE;
(* an error occured on K-Bus*)
(* request vaules for ErrCode and ErrArg *)
CASE k_bus_err_code OF
0 : return;
(* should not happen, though an error occured *)
1 : CASE k_bus_arg OF
0 : report error;
(* EEPROM checksum error *)
1 : report error;
(* overflow in code buffer *)
2 : report error;
(* unknown datatype *)
END_CASE;
2 : CASE k_bus_arg OF
0 : report error;
(* programmed configuration, wrong table entry *)
ELSE report error;
(* wrong table entry *)
END_CASE;
3 : report error
(* K-Bus command error *)
4 : CASE k_bus_arg OF
0 : report error;
(* break after power supply *)
ELSE report error;
(* break after terminal 'k_bus_arg' *)
END_CASE;
5 : report error
(* K-Bus-error during register-communication with
9 : CASE k_bus_arg OF
0 : report error; (* checksum error in program flash *)
ELSE report error;
44
(* terminal 'k_bus_arg' does not exist in boot
configuration *)
Embedded PC
END_CASE;
14 : report error
(* 'k_bus_arg'-th terminal has wrong format *)
15 : report error
(* wrong number of bus terminals *)
16 : report error
(* length of K-Bus data is invalid *)
END_CASE
(* reset bus, if reason for error is removed, bus
starts again *)
To make the control work, the register and the program must be linked in System Manager. If the PLC program is
attached in System Manager the following signals are available:
Analog the registers of the terminal bus are shown in System Manager:
Link signals and variables:
k_bus_err_code with
ErrorCode
k_bus_err_arg
with
ErrorArg
k_bus_state
with
BusState
k_bus_request
with
Request[0]
and
If all signals are linked the programmer can load configuration and PLC program onto the system.
Embedded PC
45
Decomissioning
6. Decomissioning
A CX9000 hardware configuration is dismantled in 2 stages:
Before a CX-System can be dismantled, the system should be switched off, and the power supply should be
disconnected.
Before the individual CX-System modules are disconnected, the whole CX- hardware block should be removed from
1.2. Releasing the CX-System
46
Embedded PC
Decomissioning
2. Separating the individual modules
2.1. Separating the power supply unit, the CX-System CPU and other components
Place the CX-block onto a suitable support with the front facing down. Then insert a flat screwdriver with dimensions
1.0 x 5.5 x 150 mm into the locking mechanism, and then operating the slider by turning it about 90 degrees. The
locking mechanism on the rear affects an approx. 2-3 mm wide clearance of the module latching mechanism,
pushing them apart. The plug connectors of the PC 104 interface can then be pulled apart carefully.
Only modules (CPU, fieldbus connections and UPS modules) that can be separated non-destructively feature a
release device. Modules that cannot be separated only feature a marking point (with or without red paint seal).
Applying force to these elements will destroy them.
Warning
Forcibly opening the module housing (e.g. removing the cover) will destroy the housing.
Disposal
The device must be fully dismantled in order to dispose of it.
Electronic parts must be disposed of in accordance with national electronics scrap regulations.
Embedded PC
47
Appendix
7. Appendix
Update Image
General
Warning
In general an update of the image is not necessary: The basic functionality of TwinCAT and
TwinCAT PLC are working fine.
Update the Image ONLY if there is an advice from BECKHOFF Automation GmbH. Never
If the image update is required, here some basic information for overview:
One single file " BOOT.BIN " is required to update the image : BOOT.BIN contains full CE operating system
but also the TwinCAT functionality.
This single file can NOT just xcopied to the target CX9000 device
Note
There are two ways to update the image of the CX9000-System:
1.
via Image-Server
2.
interactive tool on CX9000
Short description:
The general steps to update an CX9000-image are:
1.
download the new image and the required tool from BECKHOFF FTP server
2.
provide the new image on the host PC (notebook, PC ..)
3.
start the image-server-tool on the host pc: this tool is listening on network to be connected from CX9000
device.
4.
The initial activity to get a new image is started by the CX9000 device: This will happen if CX9000 is
configured to start in boot-strap mode.
5.
after downloading the image from host pc the CX9000 will reorganize itself, this will take some time
(several minutes)
6.
You may not power cycle during this phase otherwise the device will be damaged!
7.
After all activities have been finished, power down the CX9000 device, deactivate " boot strap " and power on
device.
Update mechanism has been finished.
Step by step
1.
Images on BECKHOFF FTP
Link to CX9000 images on Beckhoff FTP Server:
For CX9001-x00x (32 MB flash) use CX9000 HMI:
ftp.beckhoff.com/Software/embPC-Control/CE/Platforms/CX1800-0101-0003_HMI
48
For CX9000-x00x (16 MB flash) use CX9000 LF:
ftp.beckhoff.com/Software/embPC-Control/CE/Platforms/CX1800-0100-0003_LF
The tool " Image-Server " for host PC is available in both HMI and LF folder (same tool in two folders),
download file " CX9000_ImageUpdate.zip "
Keep the structure of the zip file when unzipping.
Embedded PC
Appendix
2. Prepare Image-Server (once)
Provide the image server on the host PC, the components are:
Two batchfiles " CxImgSrv_HMI.bat " and " CxImgSrv_LF.bat "
Note that the CX9000 is shipped with different hardware environment (e.g. more or less flash memory).
Folder " \Tools " contains the image server itself: CxImageSrv.exe
Folder " \Images " contains the HMI and LF subfolders with the required file " Boot.bin "
If you receive a new NK.BIN file, just rename it to " Boot.bin " and provide it in the correct subfolder
3. Prepare CX9000
Prepare the " Boot-Strap Mode " on CX9000. There are two ways to set the CX9000 into " Boot-Strap Mode " :
set a DIP-switch on CX9000
start a program, to set the CX9000 into " Boot-Strap Mode " .
Prepare the CX9000 to start in " boot-strap " mode.
1.
2.
3.
Find the dip switches 1,2,3,4 and set switch 3 from OFF to ON
Alternative the administrator can start a tool on the CX-Systems to set the CX9000 into " Boot-Strap Mode " . First the
program must be downloaded from the BECKHOFF FTP-Server. If the CX9000 has no USB the tool can be
transferred via ftp onto the system. Use CERHOST-Tools to control the CX9000 remote via Ethernet. Activate the
FTP server on the CX, if not it is disabled. The necessary configuration is shown below:
Embedded PC
49
Appendix
It is a good idea to choose " \Temp " or " \Public " as target directory, though this range is mapped into the RAM regions
instead of the hard disc located in flash memory. For operation the system must be rebooted.Just follow the
instructions on the screen. After restart of the CX9000 the program can be copied easily to the CX9000 with the
explorer:
50
Embedded PC
Appendix
Warning
Via CERHOST the program will be started with a double click on the icon. Warning: Do NOT
start the program if you have no image-Server ( see below) AND a correct image!
The CX9000 is now no longer useable for PLC until an update was made!
The reset to operational is done automatically if the the update has taken place.
connect CX9000 to ethernet network
Note
Image server will listen in complete network to be contacted by CX9000
Two solutions to be sure that you just update your CX9000 device.... and not others in
network !
(for details see network notes below)
4. Start image server
Start the image server on the host PC:
start the correct batch file " CxImgSrv_HMI.bat " or " CxImgSrv_LF.bat " (to let image-server provide the HMI
or the LF image in network)
The batch file will start a command-shell and prompt : " Waiting for download request... "
5. Phases during image update
Start CX90x0 to initiate the download procedure :
Initial phase :
Start CX90x0 to initiate the download procedure :power on CX90x0
The CX90x0 tries to find an image server on network to download an image.
Download phase :
Image server will prompt a message in command shell if an image is downloaded to CX90x0
Message is like :
Boot image request from device CX90x0_BA23
Working directory is Image\HMI
Calling TFTP.exe -i & lt; CX90x0-IP & gt; PUT boot.bin
On CX90x0 the HDD led will light up : The CX- device is erasing and copying new image.
Reorganisation phase :
The image server will prompt a message, that the download of new image has been finished.
Now, close command shell. (Press & lt; CTRL & gt; + & lt; c & gt; or close the window)
Set system back to operation mode; to avoid the system to run the update procedure again.
Set the dip switch 3 back to " off " and close the battery compartment.
Embedded PC
51
Appendix
7. Finish Update
Update is now complete. Reconnect the CX90x0-System to the network. The CX-System can now be used as before.
NOTES on network configuration:
Two solutions to be sure that you just update your CX9000 device.... and not others in network !
1a.
provide a subnet (like a second network card in host PC)
or
1b.
connect host-pc and CX9000 directly without involving company network
or
2.
The image server can be configured to let CX directly request image from specific IP address.
Step 1: connect CX9000 with PC, get IP address of PC like 192.16.18.123
Step 2: edit the image-server-batch-file and add the IP address to the commandline. (Sample : Tools\CxImageSrv
Images\HMI 192.16.18.123 )
Step 3: proceed with booting CX9000 in boot strap mode. Now the CX will try do request image from IP address
192.16.18.123
Warning
The CX90x0 is still working to initialize the flash ! DO NOT POWER DOWN THE CX90x0 !
Wait until CX90x0 PWR led is BLUE
it has finished update!
52
or GREEN again: The device will reboot after
Embedded PC
Appendix
Interactive tool on CX9000:
First the program " Cx9ImageUpdate.exe " must be downloaded from BECKHOFF FTP-Server. If the CX9000 has no
USB the tool can be transferred via ftp onto the system. Use CERHOST-Tools to control the CX9000 remote via
Ethernet. Activate the FTP server on the CX, if not it is disabled. The necessary configuration is shown below:
explorer:
Embedded PC
53
Appendix
If there is enough free space on the CX9000 (big memory) the image can be copied together with to tool. Otherwise
the image file can be accessed via network drive. In this case you should map the drive to the CX9000:
If the image is copied to the CX9000 or the network drive is mapped to the system the update tool can be started by
double click on the icon. The program ask for the filename of the image. The complete path to the file must be
entered now. Depending on the network configuration the password is requested again.
54
Embedded PC
Appendix
After click on " FLASH IMAGE " button a request box appears to confirm the image file. This is the last chance to
abort the update process.
When confirming the image file a warning appears on the screen.
The progress is shown in the status line in the bottom of the tool.
When the update is complete the following message appears in the status field:
Embedded PC
55
Appendix
The CX9000 can be rebooted now. If the system has started again it can be used as before. The update tool and the
image are removed if they were copied on the RAM drive.
56
Embedded PC
Appendix
Accessories
Compact flash cards
order number
Description
CX1900-0023
1 GByte compact flash card type I
CX1900-0025
2 GByte compact flash card type I
CX1900-0027
4 GByte compact flash card type I
Connectors and Adaptors
order
Description
number
CX1900-0101
Labeling Tags
order number
CX1900-0200
DVI-to-VGA passive Adaptor for connecting a standard desktop VGA monitor to the
CX-System
– singles out the VGA signals of the DVI-I interface
– 29-pin male DVI-A connector (bottom) to 15-pin female connector (top)
– weight approx. 40 g
– dimensions (W x H x D) 40 x 42 x 15 mm
Description
Universal plastic labels for the CX-System (package contains 1000 labels)
– snaps into the premoulded spots on the CX-System components
– labeling can be done with a X-Y plotter
– dimension of the single label 15 x 5 mm
– material: white colored plastic
– Murrplastik type KMR 5/15, order number 86401014
replacement battery for CX-System
order number
Description
CX1900-0102
Embedded PC
Battery for das CX-System
- original product description: Panasonic type CR2032 3V/225mAh
57
Appendix
Certifications
All products of the Embedded PC family are CE, UL and GOST-R certified. Since the product family is continuously
developed further, we are unable to provide a full listing here. The current list of certified products can be found on
the Embedded PC certificates web page or at www.beckhoff.de under Embedded PC.
58
Embedded PC
Appendix
Support and Service
Beckhoff and their partners around the world offer comprehensive support and service, making available fast and
competent assistance with all questions related to Beckhoff products and system solutions.
Beckhoff Support
Support offers you comprehensive technical assistance, helping you no only with the application of individual
Beckhoff products, but also with other, wide-ranging services:
world-wide support
design, programming and commissioning of complex automation systems
and extensive training program for Beckhoff system components
Hotline:
+49(0)5246/963-157
Fax:
+49(0)5246/963-9157
e-mail:
support@beckhoff.com
Beckhoff Service
The Beckhoff Service Center supports you in all matters of after-sales service:
on-site service
repair service
spare parts service
hotline service
Hotline:
+49(0)5246/963-460
Fax:
+49(0)5246/963-479
e-mail:
service@beckhoff.com
You will find further support and service addresses on our Internet pages under http://www.beckhoff.com.
Beckhoff Headquarters
Eiserstr. 5
33415 Verl
Germany
Phone:
+49(0)5246/963-0
Fax:
+49(0)5246/963-198
e-mail:
info@beckhoff.com
The addresses of Beckhoff's branch offices and representatives round the world can be found on her internet pages:
You will also find further documentation for Beckhoff components there.
Embedded PC
59