307_USER.pdf
Wybór agregatu prądotwórczego 3f z SZR do sklepu spożywczego 17kW
Przecież te które masz to są cyfrowe. Czyli przedłużenie tego wszystkiego o 30m nie powinno zaszkodzić? Wydaje mi się, że w instrukcji od sterownika jest mowa o czyjnikach analogowych i cyfrowych Wiem że nie są mechaniczne na linkę ale chyba niekoniecznie cyfrowe? instrukcja w załączniku
Pobierz plik - link do postu
DKG-307 User Manual
V-42 (24.05.2013)
DKG-307 AUTOMATIC
MAINS FAILURE UNIT
CANBUS AND MPU VERSIONS
DESCRIPTION
The controller is a comprehensive AMF unit for
single genset standby or dual genset mutual standby
operations.
The unit is available with MPU or CANBUS versions.
The CANBUS version connects to ECU controlled
electronic engines providing engine control,
protection and instrumentation without extra senders.
The unit is able to initiate modem calls and send
SMS messages in fault conditions through external
modems.
The unit provides a comprehensive set of digitally
adjustable timers, threshold levels, input and output
configurations, operating sequences and engine
types. All programs may be modified via front panel
pushbuttons, and do not require an external unit.
Last 100 faults are stored in the event log file. The
event log includes not only the date-time information,
but also a comprehensive list of measured genset
parameters at the time that the fault has occurred.
The WINDOWS based RAINBOW program allows
remote monitoring and control.
The unit supports MODBUS protocol enabling
communication with PLCs and building management
systems. The MODBUS protocol is also supported
through GSM and PSTN modems.
FEATURES
True RMS measurements
ECU connection through J1939 CAN option
MPU input option
Dual genset mutual standby operation
Event logging with time stamp and
measurements
Battery backed-up real time clock
Built in daily / weekly / monthly exerciser
Weekly operation schedule programs
Field adjustable parameters
RS-232 serial port
Free MS-Windows Remote monitoring SW
GSM and PSTN modem support
GSM SMS message sending on fault
MODBUS communications
Customer logo display capability
10ADC relay outputs
Configurable analogue inputs: 4
Configurable digital inputs: 7
Configurable relay outputs: 2
Total relay outputs: 6
I/O expansion capability
Plug-in connection system
DKG-307 User Manual
V-42 (24.05.2013)
TABLE OF CONTENTS
Section
1. INSTALLATION
1.1. Introduction to the Control Panel
1.2. Mounting the Unit
1.3. Wiring the Unit
2. INPUTS AND OUTPUTS
3. DISPLAYS
3.1. Led Displays
3.2. Digital Displays
4. ALARMS AND WARNINGS
5. MODES OF OPERATION
6. OTHER FEATURES
6.1. Remote start operation
6.2. Sender type selection
6.3. Engine heating operation
6.4. Engine Idle Speed Operation
6.5. Engine Block Heater
6.6. Fuel Pump Control
6.7. Mains Simulation (Disable Start)
6.8. Delayed Mains Simulation, Battery Charging
6.9. Dual Genset Mutual Standby Operation
6.10. Service Request Display
6.11. Engine Hours Meter
6.12. Date-Time Display
6.13. Display of Software Version
6.14. Modem connection
6.15. SMS message sending
6.16. Remote Monitoring and Programming
6.17. Automatic Exerciser
6.18. Resuming to factory set parameters
6.19. Gas engine fuel solenoid control
6.20. Load Shedding / Dummy Load
6.21. Fuel Theft / Fuelling Messages
6.22. Firmware Update
6.23. Changing the Default Engine Speed in Volvo Engines
6.24. Engine Control Mode
6.25. Dual Voltage and Frequency
6.26. Single Phase Operation
6.27. Password Operation (applicable only to DKG-317CAN/MPU)
7. J1939 ENGINE MONITORING AND CONTROL PORT
8. MODBUS COMMUNICATION
9. WEEKLY OPERATION SCHEDULE
10. EVENT LOGGING
11. STATISTICAL COUNTERS
12. MAINTENANCE
13. PROGRAMMING
14. TROUBLESHOOTING
15. DECLARATION OF CONFORMITY
16. TECHNICAL SPECIFICATIONS
17. CONNECTION DIAGRAMS
-2-
DKG-307 User Manual
V-42 (24.05.2013)
1. INSTALLATION
1.1 Introduction to the Control Panel
The unit is a control and protection panel used in gensets. It shows the measured values on its
displays. The unit is designed to provide user friendliness for both the installer and the user.
Programming is usually unnecessary, as the factory settings have been carefully selected to fit most
applications. However programmable parameters allow the complete control over the generating set.
Programmed parameters are stored in a Non Volatile Memory and thus all information is retained even
in the event of complete loss of power.
The measured parameters are:
Mains voltage phase L1 to neutral
Mains voltage phase L2 to neutral
Mains voltage phase L3 to neutral
Mains voltage phase L1-L2
Mains voltage phase L2-L3
Mains voltage phase L3-L1
Gen voltage phase L1 to neutral
Gen voltage phase L2 to neutral
Gen voltage phase L3 to neutral
Gen voltage phase L1-L2
Gen voltage phase L2-L3
Gen voltage phase L3-L1
Gen current phase L1
Gen current phase L2
Gen current phase L3
Gen frequency
Engine speed (rpm)
Gen total kW
Gen total pf
Battery voltage,
Coolant temperature
Oil pressure
Oil temperature
Fuel level
-3-
DKG-307 User Manual
V-42 (24.05.2013)
1.2 Mounting the Unit
The unit is designed for panel mounting. The user should not be able to access parts of the
unit other than the front panel.
Mount the unit on a flat, vertical surface. Before mounting, remove the mounting brackets and
connectors from the unit, then pass the unit through the mounting opening. The unit will be maintained in
its position by the mounting brackets spring.
Engine body must be grounded for correct operation of
the unit, otherwise incorrect voltage and frequency
measurements may occur.
The output of the current transformers shall be 5 Amperes. The input current rating of the current
transformers may be selected as needed (between 10/5 and 9000/5 amps). Current transformer outputs
shall be connected by separate cable pairs from each transformer, to related inputs. Never use common
terminals or grounding. The power rating of the transformer should be at least 5 VA. It is recommended to
use 1% precision transformers.
If analogue senders (e.g. temperature, oil pressure or fuel level) are connected to the unit, it is not
possible to use auxiliary displays, otherwise the unit may be damaged. If temperature or oil pressure or
fuel level displays are already present on the generator control panel, do not connect the senders to the
unit. The unit is factory programmed for VDO type senders. However different types of senders are
selectable via programming menu. Please check the programming section.
The programmable digital inputs are compatible with both ‘normally open’ and ‘normally
closed’ contacts, switching either to BAT- or BAT+.
The charge alternator connection terminal provides also the excitation current, thus it is not
necessary to use an external charge lamp.
1.3 Wiring the Unit
WARNING: THE UNIT IS NOT FUSED.
Use external fuses for Mains phases: L1,L2,L3, Generator phase:
L1,L2,L3, Battery positive: BAT(+).
Install the fuses as nearly as possible to the unit in a place easily
accessible for the user.
The fuse rating should be 6 Amps.
WARNING: ELECTRICITY CAN KILL
ALWAYS disconnect the power BEFORE connecting the
unit.The fuse rating should be 6 Amps.
1) ALWAYS remove the plug connectors when inserting wires
with a screwdriver.
2) An appropriate and readily accessible set of disconnection
devices (e.g. automatic fuses) MUST be provided as part of
the installation.
3) The building mains supply MUST incorporate appropriate
short-circuit backup protection (e.g. a fuse or circuit breaker)
of High Breaking Capacity (HBC, at least 1500A).
-4-
DKG-307 User Manual
V-42 (24.05.2013)
RS-232 SERIAL PORT: This connector provides serial data input and output for various purposes like
remote monitoring and remote programming.
EXTENSION CONNECTOR: This connector is intended for the connection to output extension modules.
The optional relay extension module provides 8 programmable 16A relay outputs. The unit allows the use
of up to 2 I/O extension modules.
Term Function
1
GENERATOR CONTACTOR
2
3
4
5
6
7
GEN-L1
GEN-L2
GEN-L3
GENERATOR NEUTRAL
MAINS NEUTRAL
MAINS-L3
8
9
10
MAINS-L2
MAINS-L1
MAINS CONTACTOR
11
12
GROUND
BATTERY POSITIVE
13
FUEL LEVEL SENDER
14
OIL PRESSURE SENDER
15
COOLANT TEMP. SENDER
Technical data
Description
Relay output, 16A-AC This output provides energy to the generator
contactor. If the generator phases do not have
acceptable voltage or frequency values, the
generator contactor will be de-energized. In
order to provide extra security, the normally
closed contact of the mains contactor should
be serially connected to this output.
Generator phase
Connect the generator phases to these inputs.
inputs, 0-300V-AC
The generator phase voltages upper and
lower limits are programmable.
Input, 0-300V-AC
Neutral terminal for the generator phases.
Input, 0-300V-AC
Neutral terminal for the mains phases.
Mains phase inputs, Connect the mains phases to these inputs.
0-300V-AC
The mains voltages upper and lower limits are
programmable.
Relay output, 16A-AC This output provides energy to the mains
contactor. If the mains phases do not have
acceptable voltages, the mains contactor will
be de-energized. In order to provide extra
security, the normally closed contact of the
generator contactor should be serially
O VDC
Power supply negative connection.
+12 or 24VDC
The positive terminal of the DC Supply shall
be connected to this terminal. The unit
operates on both 12V and 24V battery
systems.
Input, 0-5000 ohms
Analogue fuel level sender connection. Do not
connect the sender to other devices. The input
has programmable ohms for VDO senders.
Input, 0-5000 ohms
Analogue oil pressure sender connection. Do
not connect the sender to other devices. The
input has programmable characteristics and
connects to any kind of sender.
Input, 0-5000 ohms
Analogue
high
temperature
sender
connection. Do not connect the sender to
other devices. The input has programmable
characteristics and connects to any kind of
sender.
-5-
DKG-307 User Manual
V-42 (24.05.2013)
Term Function
16
CHARGE
Technical data
Input and output
17
RELAY-2 (HORN RELAY)
Output 10A/28VDC
18
RELAY-1 (STOP RELAY)
Output 10A/28VDC
19
20
21
22
23
24
25
26
27
28
29
START RELAY
FUEL RELAY
EMERGENCY STOP
SPARE-2
PROGRAM LOCK
SPARE-1
COOLANT LEVEL
HIGH TEMP
LOW OIL PRESSURE
RECTIFIER FAIL
CURR_1+
Output 10A/28VDC
Output 10A/28VDC
Digital inputs
30
CURR_1-
31
CURR_2+
32
CURR_2-
33
CURR_3+
34
CURR_3-
35
OIL TEMP. SENDER
Description
Connect the charge alternator’s D+ terminal to
this terminal. This terminal will supply the
excitation current and measure the voltage of
the charge alternator.
This relay has programmable function,
selectable from a list.
This relay controls the engine cranking.
This relay is used for fuel solenoid control.
These
inputs
have
programmable
characteristics selected via the program
menu. Each input may be driven by a
‘normally closed’ or ‘normally open’ contact,
switching either battery+ or battery-. The effect
of the switch is also selectable from a list. See
PROGRAMMING section for more details.
Current transformer Connect the generator current transformer
terminals to these inputs. Do not connect the
inputs, 5A-AC
same current transformer to other instruments
otherwise a unit fault will occur. Connect each
terminal of the transformer to the unit’s related
terminal. Do not use common terminals. Do
not use grounding. Correct polarity of
connection is vital. If the measured power is
negative, then change the polarity of each 3
current transformers. The rating of the
transformers should be the same for each of
the 3 phases. The secondary winding rating
shall be 5 Amperes. (For ex. 200/5 Amps).
Input, 0-5000 ohms
Analogue oil temperature sender connection.
Do not connect the sender to other devices.
The input has programmable characteristics
and connects to any kind of sender.
CANBUS VERSIONS
36
37
CANBUS-L
CANBUS-H
36
37
MPU MPU +
Digital communication Connect the J1939 port of an electronic
port
engine to these terminals.
The 120 ohm terminating resistors are inside
the unit. Please do not connect external
resistors.
Use a twisted cable pair or coaxial cable for
best results.
MPU INPUT VERSIONS
Analog input, 0.5 to Connect the MPU unit to these inputs
30V-AC
best results.
-6-
DKG-307 User Manual
V-42 (24.05.2013)
3. DISPLAYS
3.1 Led Displays
The unit has 12 LEDs, divided in 3 groups:
-Group_1: Operating mode: This group indicates the genset function.
-Group_2: Mimic diagram: This group indicates the current status of the mains and genset
voltages and contactors.
-Group_3: Warnings and alarms: This group indicates the existence of abnormal conditions
encountered during operation.
Function
MAINS ON
Color
Green
MAINS OFF
Red
LOAD MAINS
LOAD GENERATOR
GENERATOR
Green
Yellow
Yellow
TEST
Yellow
RUN
Yellow
STOP
Yellow
AUTO
Green
WARNINGS & ALARMS
Red
SERVICE REQUEST
Red
Description
The LED will turn on when all 3 mains phase voltages
are within the limits.
The LED will turn on when at least one of the mains
phase voltages is outside limits.
It turns on when the mains contactor is activated.
It turns on when the generator contactor is activated.
The LED will flash when the engine is running. It will
turn on steadily when all 3 generator phase voltages
are within the programmed limits.
It turns on when the related operation mode is
selected. One of these LEDs is always on and
indicates which operation mode is selected.
If the operation of the genset is disabled by the
weekly operation schedule, then the AUTO led will
flash.
If a fault condition resulting to the engine shutdown or
loaddump condition has occurred, the related alarm
led turns on steadily. If a warning condition occurs,
this led will flash. Alarms work on a first occurring
basis. The occurrence of a fault will disable other
faults of lower or equal priority.
Engine periodic maintenance request indicator. It
turns on when the preset engine hours or time
duration after previous service has elapsed.
-7-
DKG-307 User Manual
V-42 (24.05.2013)
3.2 Digital Displays
The unit has 3 seven segment displays. They show:
-Measured parameters,
-Service counters,
-Statistical counters,
-Program parameters.
The navigation between different screens in a group is made with the MENU► button.
Holding the MENU► button pressed for 1 second makes the display to switch to the next group.
VOLTAGE DISPLAY: This display shows:
-phase R voltage if the load is on mains
-Phase U voltage if the load is on the genset
By pressing the MENU key, below values may be displayed:
-(L1-L2-L3) mains phase to neutral voltages
-(L1-L2-L3) generator phase to neutral voltages
-(L12-L23-L31) mains phase to phase voltages
-(L12-L23-L31) generator phase to phase voltages
If the service counters group is displayed, then this display will show the counter name.
In programming mode it displays (PGM).
CURRENT DISPLAY: This display will show the current values measured using the current
transformers. Using the programming menu, current transformers within the range of 10/5A to 9000/5A
may be programmed.
In programming mode it displays the program number.
MULTIFUNCTION DISPLAY: By pressing the MENU key below values may read:
-oil pressure (bar)
-coolant temperature (ºC)
-fuel level
-generator frequency (Hz)
-generator active power (KW)
-battery voltage (V-DC),
In programming mode it displays the program value.
-8-
DKG-307 User Manual
V-42 (24.05.2013)
Alarms indicate an abnormal situation in the generating set are divided into 3 priority levels:
1- ALARMS: These are the most important fault conditions and cause:
- Therelated ALARM led to be on steadily,
- The genset contactor to be released immediately,
- The engine to be stopped immediately,
- The Horn, Alarm, Alarm+Load_dump and Alarm+Load_dump+Warning digital
outputs to operate, (if selected via programming menu)
2- LOAD_DUMPS: These fault conditions cause:
- The engine to be stopped after Cooldown period,
- The Horn, Alarm+Load_dump and Alarm+Load_dump+Warning digital outputs to
3- WARNINGS: These conditions cause:
- Therelated ALARM led to flash,
- The Horn and Alarm+Load_dump+Warning digital outputs to operate, (if selected
If the ALARM MUTE button is pressed, the Horn output will be deactivated; however the
existing alarms will persist and disable the operation of the genset.
Alarms operate in a first occurring basis:
-If an alarm is present, following alarms, load_dumps and warnings will not be accepted,
-If a load_dump is present, following load_dumps and warnings will not be accepted,
-If a warning is present, following warnings will not be accepted.
Alarms may be of LATCHING type following programming. For latching alarms, even if the alarm
condition is removed, the alarms will stay on and disable the operation of the genset. The existing alarms
may be canceled by pressing one of the operating mode buttons (LOAD TEST / TEST / OFF / AUTO).
Most of the alarms have programmable trip levels. See the programming chapter for adjustable
alarm limits.
-9-
DKG-307 User Manual
V-42 (24.05.2013)
LOW OIL PRESSURE: Set if a signal is detected at the Low Oil Pressure Switch input or the oil
pressure value measured from the sender is below the programmed limit. Warning and alarm limits are
separately programmable for the oil pressure sender input. This fault will be monitored with Holdoff
Timer delay after the engine is running. Also if the oil pressure switch is open at the beginning of a start
attempt, then the engine will not be started and the oil pressure alarm led will flash. When the oil
pressure switch closes, normal operation will be resumed.
HIGH TEMPERATURE: Set if a signal is detected at the High Temperature Switch input or the coolant
temperature value measured from the sender is above the programmed limit. Warning and alarm limits
are separately programmable for the temperature sender input.
LOW TEMPERATURE (warning) : Set if the coolant temperature value measured from the sender is
blow the Engine Heating Temperature limit.
LOW SPEED / HIGH SPEED: Set if the generator frequency or rpm is outside programmed limits.
These faults will be monitored with Holdoff Timer delay after the engine is running. Low and high limits
for warning and alarm are separately programmable. Another high shutdown limit which is 12% above
the high limit is always monitored and stops the engine immediately.
START FAIL (alarm): Set if the engine is not running after programmed number of start attempts.
STOP FAIL (warning): Set if the engine has not stopped before the expiration of the Stop Timer.
ECU FAIL (warning): Set when an engine fault code is received from the ECU of the electronic engine.
This fault will not cause an engine stop. If necessary, the engine will be stopped by the ECU.
ECU FAIL (alarm): Set if no information has been received during 3 seconds from the ECU of the
electronic engine. This fault condition is only controlled if fuel is on.
OVERLOAD (load_dump): Set if at least one of the genset phase currents goes over the Overcurrent
Limit for Overload Timer. If currents go below the limit before expiration of the timer then no alarm will
be set.
EXCESS POWER (load_dump): Set if the genset power (KW) supplied to the load goes over the
Excess Power limit for Overload Timer. If the power goes below the limit before expiration of the timer
then no alarm will be set.
GENSET LOW VOLTAGE: Set if any of the generator phase voltages goes outside programmed limits
for Overload Timer. This fault will be monitored with holdoff timer delay after the engine is running.
GENSET HIGH VOLTAGE: Set if any of the generator phase voltages goes outside programmed limits
LOW COOLANT LEVEL: Set if a signal is detected at the low coolant level input.
HIGH BATTERY VOLTAGE: Set if the battery voltage goes above programmed limits. Both warning and
alarm levels for high battery voltage are programmable.
LOW BATTERY VOLTAGE (warning): Set if the battery voltage goes below the programmed limit.
During engine cranking this fault is not monitored.
CHARGE: Set if a charge alternator failure (or broken belt) occurs. This fault condition may result to a
warning or alarm following programming.
RECTIFIER FAIL: Set if a signal is detected at the rectifier fail input. This input is only monitored when
mains voltages are present.
EMERGENCY STOP: Set if a signal is detected at the emergency stop input.
SPARE: Set if a signal is detected from the related spare fault input.
- 10 -
DKG-307 User Manual
V-42 (24.05.2013)
The modes of operation are selected by pushing the front panel keys. Changing the operation
mode while the genset is running will result into a behavior suitable for the new operating mode. For
example, if the TEST mode is selected when genset is running at RUN mode, then the genset will take
the load.
STOP: In this mode, the mains contactor will be energized if mains phase voltages are within the
programmed limits. The engine will be stopped.
AUTO: It is used for genset and mains automatic transfer. If at least one of the mains phase voltages is
outside limits, the mains contactor will be deactivated.
The diesel will be started for programmed times after the preheat timer. When the engine runs, the crank
relay will be immediately deactivated. The engine will run without load during engine heating period. After
this, if alternator phase voltages and frequency are within limits, then the unit will wait for the generator
contactor period and the generator contactor will be energized.
When all the mains phase voltages are within the limits, the engine will continue to run for the mains
waiting period. At the end of this period the generator contactor is deactivated and the mains contactor will
be energized. If a cooldown period is given, the generator will continue to run during cooldown period. At
the end of the period, the fuel solenoid will be de-energized and the diesel will stop. The unit will be ready
for the next mains failure.
If the operation of the genset is disabled by the weekly schedule, then the AUTO led will flash, and the
operation of the genset will be as in the OFF mode.
RUN: It is used to test the generator when the mains are on, or keep the generator running in the
emergency backup mode. The operation of the generator is similar to the AUTO mode, but the mains
contactor will not be deactivated if the mains are not off. If the mains are off, mains contactor will be
deactivated and the generator contactor will be activated. When the mains are on again, a changeover to
the mains will be made, but the engine will be kept running unless another mode is selected. To stop the
engine, select AUTO or OFF mode.
TEST: It is used to test the genset under load. Once this mode is selected, the engine will run and the
load will be transferred to the genset. The genset will feed the load indefinitely unless another mode is
selected.
- 11 -
DKG-307 User Manual
V-42 (24.05.2013)
6. OTHER FEATURES
6.1 Remote Start Operation
The unit offers the possibility of REMOTE START mode of operation. The SPARE-2 input may
be assigned as Remote Start Input using the program parameter P_083.
The REMOTE START signal may be a NO or NC contact, switching to either battery positive or
battery negative. These selections are made using programming menu.
It is also necessary to set the ACTION program parameter of the SPARE-2 input to 3 in order to
prevent any alarm from this input.
In this mode the mains phases are not monitored. If the REMOTE START signal is present
then the mains will be supposed to fail, inversely if the REMOTE START signal is absent, then mains
voltages will be supposed to be present. The front panels mimic diagram’s mains LEDs will reflect the
status of the REMOTE START input.
6.2 Sender type Selection
The unit has the ability to adapt to any type of oil pressure and temperature senders. The
commonly used standard sender characteristics are recorded in memory and selectable from a list.
However non standard senders may also be used by entering their characteristics to the table.
Oil Pressure Sender Type Selection:
Selectable sender types are:
0: Sender characteristics are defined in Sender Characteristics table.
1: VDO 0-7 bars (10-180 ohms)
2: VDO 0-10 bars (10-180 ohms)
3: DATCON 0-7 bars (240-33 ohms)
4: DATCON 0-10 bars (240-33 ohms)
5: DATCON 0-7 bars (0-90 ohms)
6: DATCON 0-10 bars (0-90 ohms)
7: DATCON 0-7 bars (75-10 ohms)
Temperature Sender Selection:
1: VDO
2: DATCON DAH type
3: DATCON DAL type
Fuel Level Sender Selection:
The Fuel Level Sender characteristic is programmable through table.
Oil Temperature Sender Selection:
1: VDO
2: DATCON DAH type
3: DATCON DAL type
- 12 -
DKG-307 User Manual
V-42 (24.05.2013)
6.3 Engine Heating Operation
Especially on engines without a body heater, or with a failing one, it may be desired that the
genset should not take the load before reaching a suitable temperature. The unit offers 2 different
ways of engine heating.
1. Timer controlled heating:
This operation mode is selected when the Engine Heating Method parameter is set to 0. In this
mode, the engine will run during parameter Engine Heating Timer, and then the genset will take the
load.
2. Timer and temperature controlled heating:
This operation mode is selected when the Engine Heating Method parameter is set to 1. In this
mode, at first the engine will run during parameter Engine Heating Timer, then it will continue to run
until the measured coolant temperature reaches the limit defined in parameter Engine Heating
Temperature. When the requested temperature is reached, the load will be transferred to the genset.
This operation mode may be used as a backup to the engine body heater. If the engine body is warm
the heating will be skipped.
6.4 Engine Idle Speed Operation
It may be required that the engine runs at the idle speed for a programmed duration for engine
heating. The idle operation duration is adjusted with the parameter Idle Speed Timer. The idle speed
will be set by the governor control unit of the engine.
Any of the spare relay outputs may be assigned as IDLE output using Relay Definition
program parameters. Also relays on an extension module may be assigned to this function.
The Idle speed operation is performed both in engine start-up and cool-down sequences.
Speed and voltage protections are disabled during idle speed operation.
6.5 Engine Block Heater
The unit is able to provide a relay output in order to drive the block heater resistor. The
temperature reference is the coolant temperature measured from the the analog sender input.
The block heater relay function may be assigned to spare relays using Relay Definition
The engine body temperature limit is adjusted using the parameter Engine Heating
Temperature. The same parameter is used for engine heating operation.
The relay will become active if the body temperature falls to 4 degrees below the limit set by
Engine Heating Temperature. It turns off when the body temperature exceeds Engine Heating
Temperature.
- 13 -
DKG-307 User Manual
V-42 (24.05.2013)
6.6 Fuel Pump Control
The unit is able to provide a relay output in order to drive the fuel pump motor. The fuel pump
is used in order to transfer fuel from the large capacity main tank (if exists) to the genset daily tank
which is generally integrated in the chassis and has a limited capacity.
The fuel level reference is measured through the analog fuel level sender. When the
measured fuel level falls below Fuel Pump Low Limit parameter, the fuel pump relay output will
operate. When the fuel level reaches Fuel Pump High Limit parameter, the relay will turn off. Thus
the chassis fuel tank level will be always kept between Fuel Pump Low Limit and Fuel Pump High
Limit parameters.
The fuel pump relay function may be assigned to spare relays using Relay Definition program
6.7 Mains Simulation (Disable Start)
The unit offers an optional SIMULATE MAINS signal input. The SPARE-2 digital input may be
assigned as Simulate Mains using program parameter P_084.
It is also necessary to set the ACTION program parameter of the related input to 3 in order to
prevent any alarms generated from this input.
The SIMULATE MAINS signal may be a NO or NC contact, switching to either battery positive or
battery negative. These selections are made using the programming menu.
If the Simulate Mains input is defined and the input signal is active, the mains phases are not
monitored and supposed to be inside limits. This will prevent the genset from starting even in case of a
mains failure. If the genset is running when the signal is applied, then usual Mains Waiting and
Cooldown cycles will be performed before engine stop. When the SIMULATE MAINS signal is present,
the front panels mimic diagram’s mains LEDs will reflect the mains voltages as present.
When the signal is passive, the unit will revert to normal operation and monitor the mains
voltage status.
The REMOTE START operation overrides SIMULATE
MAINS and FORCE TO START operations.
- 14 -
DKG-307 User Manual
V-42 (24.05.2013)
6.8 Delayed Mains Simulation, Battery Charging
The Delayed Mains Simulation feature is used in battery backed up telecom systems where
batteries are able to supply the load during a certain period. The genset is requested to run only when
battery voltage drops below the critical level. Once the engine runs, the rectifier system starts charging
the batteries and the battery voltage goes up immediately. Thus the engine should continue to run a
programmed period for effective charging. The critical battery voltage level will be detected by an
external unit which provides the digital Simulate Mains signal for the genset control unit.
If the Delayed Simulate Mains program parameter (P_085) is set to 1 and the input signal is
active when the genset is not feeding the load, the mains phases are not monitored and supposed to
be inside limits. This will prevent the genset from starting when the simulate mains signal is present
(batteries charged). The genset will start when mains voltages are out of limits and the simulate mains
signal not present.
If the genset is running when the signal is applied, then MAINS SIMULATION will be
prevented during P_086 Flashing Relay Timer program parameter. After this, usual Mains Waiting
and Cooldown cycles will be performed before engine stop. When the SIMULATE MAINS signal is
present, the front panels mimic diagram’s mains LEDs will reflect the mains voltages as present.
voltage status.
The REMOTE START operation overrides DELAYED
SIMULATE MAINS operation. When both parameters
“Remote Start Operation” and “Delayed Simulate
Mains” are set then REMOTE START operation mode is
performed.
- 15 -
DKG-307 User Manual
V-42 (24.05.2013)
6.9 Dual Genset Mutual Standby Operation
Dual genset intermittent operation consists of regular switching of the load between 2 gensets.
The use of 2 gensets instead of one is due either to safety purposes in case of a genset failure or to a
continuous operation requesting service stops.
The running period for each genset is adjustable using Flashing Relay Timer program
parameter. If the time is adjusted as 0 hours, it will be actually set to 2 minutes for faster testing
purposes.
A flashing relay output function is provided, based on the parameter Flashing Relay Timer.
Each time the period programmed using Flashing Relay Timer elapses, the relay output will change
position.
The flashing relay function may be assigned to spare relays using Relay Definition program
The dual genset intermittent operation uses also the Mains Simulation feature. Please review
chapter 6.7 for a detailed explanation of this feature.
Please contact DATAKOM for a complete application
manual.
- 16 -
DKG-307 User Manual
V-42 (24.05.2013)
6.10 Service Request Display
This led is designed to help the periodic maintenance of the genset to be made consistently.
The periodic maintenance is basically carried out after a given engine hours (for example 200
hours), but even if this amount of engine hours is not fulfilled, it is performed after a given time limit (for
example 12 months).
The SERVICE REQUEST led has no effect on the
genset operation.
The unit has both programmable engine hours and maintenance time limit. The engine hours is
programmable with 50-hour steps, the time limit is programmable with 1 month steps. If any of the
programmed values is zero, this means that the parameter will not be used. For example a maintenance
period of 0 months indicates that the unit will request maintenance only based on engine hours, there will
be no time limit. If the engine hours is also selected as 0 hours this will mean that the SERVICE
REQUEST display will be inoperative.
When the engine hours OR the time limit is over, the SERVICE REQUEST led (red) will start to
flash and the service request relay function will be active.
The service request relay function may be assigned to spare relays using Relay Definition
To turn off the SERVICE REQUEST led, and reset the
service period, press together the ALARM MUTE and
LAMP TEST keys for 5 seconds.
The remaining engine hours and the remaining time limit are kept stored in a non-volatile memory
and are not affected from power supply failures.
The time and engine hours to service are displayed in the STATISTICAL COUNTERS menu.
- 17 -
DKG-307 User Manual
V-42 (24.05.2013)
6.11 Engine Hour Meter
The unit features a non-erasable incremental engine hour meter. The hour meter information is
kept in a non-volatile memory and is not affected from power supply failures.
The engine hours may be displayed STATISTICAL COUNTERS menu.
6.12 Date & Time Display
The date & time display is provided for verification.
6.13 Software Version Display
Some additional features are installed within consecutive software releases. In order to be
sure of the validity of the status of the unit, the software version needs to be known.
The software version of the unit is displayed together with the data – time information.
The software version consists of 2 numbers. The first number represent the operating software
version of the unit.
6.14 Modem Connection
The unit is capable of making modem calls in case of alarm, as well as answering modem
calls made from a remote location. GSM modems and classic cable network (PSTN) modems are
acceptable.
If the modem is connected to the unit, the Modem Enable program parameter should be set
to 1, otherwise faulty operation may occur.
A maximum of 2 telephone numbers can be defined for outgoing modem calls. In case of
alarm, the unit will attempt to reach control centers associated with each number. In case of modem
connection failure, the call will be repeated up to 30 times with 2 minute intervals.
If Modem Enable or SMS Enable or MODBUS Address
parameters are different from zero, the local PC
connection will not work.
Advised modems are DATAKOM types which are powered up from the same DC battery
voltage than the unit. Most of other desktop modems with standard AT commands are also usable, but
it is the user’s responsibility to provide an uninterrupted AC supply source to the modem. The
necessary modem cable will be supplied by DATAKOM.
Modem calls are always terminated by the central RAINBOW software. However the unit does
not allow connection durations exceeding 2 minutes, and hangs up the modem when this period
expires.
The PC program used for remote monitoring and programming is the same RAINBOW
software used for RS-232 connection.
Please note that the modem operation is also compatible with the MODBUS communication.
Thus the unit can iniate and receive calls to/from a MODBUS master station. Please review chapter_8
for more details on MODBUS communication.
- 18 -
DKG-307 User Manual
V-42 (24.05.2013)
6.15 SMS Message Sending
The GSM SMS sending is activated by setting the SMS Enable program parameter to 1.
When a fault condition occurs, the unit will compose an SMS message and will send it to up to 6
phone numbers. If modem is enabled, only 4 telephone numbers are available for SMS sending.
The unit is also able to send SMS messages in below conditions, without creating a visible alarm
or warning:
Mains Fail, Mains Restored (enabled via SMS on Mains Change program parameter)
Fuel Theft, Fuelling (enabled by setting the Fuel Consumption / Hour parameter to other than 0)
If both modem and SMS are enabled, the unit will send SMS messages first and attempt modem
connection afterwards.
The maximum number of alarms transmitted in a SMS message is 4. This limitation is due to the
maximum length of an SMS message which is 160 characters.
A sample GSM SMS message is given below:
DKGxxx & lt; SITE-ID & gt;
STOP :LOW OIL PRESSURE SW.
END OF ALARM LIST
The first line of the message carries information about the unit type and the site identity string.
This line is intended for the identification of the genset sending the SMS message.
Each following line will give one fault information. The message will always be terminated by the
“END OF ALARM LIST” string.
When the message is sent, the existing alarms will be masked, causing the audible alarm relay to
release and preventing consecutive GSM SMS messages. Any new upcoming alarm will result in a new
GSM SMS message. The new message will indicate all existing alarms, even masked ones.
The necessary GSM modem cable will be supplied by DATAKOM. This is the same cable as
PSTN (land) modems.
- 19 -
DKG-307 User Manual
V-42 (24.05.2013)
6.16 Remote Monitoring and Programming
Thanks to its standard serial RS-232 port, the unit offers the remote monitoring and
programming feature.
The remote monitoring and programming PC software is called RAINBOW and may be
downloaded from www.datakom.com.tr internet site with password login.
The modem, SMS and Modbus modes are not compatible with the local PC connection. Modem
Enable, SMS Enable and MODBUS Address program parameters should be set to 0 before
connection.
The RAINBOW software allows the visualization and recording of all measured parameters.
The recorded parameters may then be analyzed graphically and printed. The software also allows the
programming of the unit and the storage of the program parameters to PC or the downloading of
stored parameters from PC to the unit.
For PCs without a serial port, below USB to serial adapters are tested and approved :
DIGITUS USB 2.0 TO RS-232 ADAPTER (PRODUCT CODE: DA70146 REV 1.1)
DIGITUS USB 1.1 TO RS-232 ADAPTER (PRODUCT CODE: DA70145 REV 1.1)
FLEXY USB 1.1 TO SERIAL ADAPTER (PRODUCT CODE BF-810)
CASECOM USB TO SERIAL CONVERTER (MODEL: RS-01)
The necessary PC connection cable will be supplied by DATAKOM. The cable length should
not be over 3 meters.
- 20 -
DKG-307 User Manual
V-42 (24.05.2013)
6.17 Exerciser
The unit offers automatic exerciser operation. The exercise operation may be done on a daily,
weekly or monthly basis.
The start day and time of the exercise is programmable as well as its duration. The exercise
may be done with or without load following programming.
Program parameters related to the exerciser are:
Exercise start day and hour
Exercise duration
Exercise off_load/on_load
Exerciser Period (Daily / Weekly / Monthly)
Please refer to the programming section for a more detailed description of the above
parameters.
When the start day and hour of exercise has come, the unit will automatically switch to either
OFF_LOAD TEST or LOAD TEST mode. The engine will run and if the on_load exercise is selected
then the load will be transferred to the genset.
If a mains failure occurs during the off-load exercise, the load will not be transferred to the
genset unless the Emergency Backup Operation is allowed by setting the related program
parameter to 1. Thus it is highly recommended that the Emergency Backup mode enabled with offload exerciser.
At the end of the exercise duration, the unit will switch back to the initial mode of operation.
If any of the mode selection keys are pressed during exercise, then the exercise will be
terminated.
Using the daily exercise mode, the unit may feed the load from the genset during predefined
hours of the day. This operation may be used in high tariff periods of the day.
In order to resume to the factory set parameter values:
-hold pressed the OFF, LAMP TEST and ALARM MUTE buttons for 5 seconds,
-“FACT RSET” will be displayed
-immediately press and hold pressed the ALARM MUTE button for 5 seconds
-factory set values will be reprogrammed to the parameter memory and “FACT RSET DONE”
will be displayed during 5 seconds.
It is not possible to restore user parameters.
- 21 -
DKG-307 User Manual
V-42 (24.05.2013)
6.19. Gas Engine Fuel Solenoid Control
The unit provides a special function for the fuel solenoid control of a gas engine.
The fuel solenoid of a gas engine is different from a diesel engine. It should be opened after
the cranking has been started and should be closed between crank cycles. The delay between the
crank start and solenoid opening is adjusted using the Gas Solenoid Delay program parameter.
The gas engine fuel solenoid relay function may be assigned to spare relays using Relay
Definition program parameters. Also relays on an extension module may be assigned to this function.
The load shedding feature consists on the disconnection of the least crucial loads when the
genset power approaches to its limits. These loads will be supplied again when the genset power falls
below the programmed limit. The internal Load Shedding function is always active. Any of the auxiliary
relays may be used as the load shedding output.
The dummy load function consists on the connection of a dummy load if the total genset load
is below a limit and to disconnection of the dummy load when the total power exceeds another limit.
The dummy load function is the inverse of the load shedding function, thus the same output may be
used for both purposes.
The parameters used in Load Shedding feature are in the Electrical Parameters Group:
Load Shedding Low Limit: If the genset active power output goes below this limit, then the Load
Shedding relay will be deactivated.
Load Shedding High Limit: If the genset active power output goes above this limit, then the Load
Shedding relay will be activated.
The unit is able to send SMS messages in fuel theft or fuelling conditions.
These SMS messages are sent without creating visible fault condition.
These features are enabled by setting the program parameter Engine Parameters & gt; Fuel
Consumption / Hour to a value other than 0%.
The Fuel Consumption / Hour parameter should be set to a value clearly greater than the
maximum fuel consumption of the engine.
If the fuel level measured from the sender input is decreased more than this parameter in 1
hour period, then a FUEL THEFT sms message is sent to programmed telephone numbers.
If the fuel level measured from the sender input is increased more than this parameter in 1
hour period, then a FUELLING sms message is sent to programmed telephone numbers.
- 22 -
DKG-307 User Manual
V-42 (24.05.2013)
The unit offers possibility of updating the firmware in the field. The firmware is updated through
the RS-232 serial port using Rainbow or a special DOS program.
The unit will go to firmware download mode with a special command from the PC program. In
download mode, the display of the unit will show “DL V1.00”
During firmware update process, the progress is visible through a percentage counter on the
screen.
The firmware update operation will take around 3 minutes.
After completion of the update a special command will set back the unit to normal operation
mode.
Volvo engines equipped with EMS-II engine control unit have the engine speed selectable
through the J1939 – CANBUS. The unit offers the possibility to the user to switch between the primary
and secondary speed using the programming menu.
If the program parameter Volvo Speed Toggle is increased, the unit will freeze for a few
seconds and switch the engine to 1800 rpm, which is generally the secondary speed. When the
parameter is decreased, the speed is set to the primary speed, which is generally 1500 rpm.
The unit must be in OFF mode, otherwise the speed
switching will not be performed.
Daha ö
mümk
Please note also that a fine adjustment of the engine speed in the ± 8 % range may be done
using the program parameter J1939 Speed Adjust.
In engine control mode, the unit is supposed to control an engine without alternator.
The engine control mode is activated by a program parameter in the Controller
Configuration group.
When the Engine Control Mode is activated:
-the unit will not display genset AC parameters (volts, amps, kW and pf).
-genset voltage and frequency protections are disabled. However engine rpm protections will
be active.
It is strongly recommended to enter correct low and
high rpm limit values in order to enable engine speed
protection.
- 23 -
Daha
mümk
DKG-307 User Manual
V-42 (24.05.2013)
The unit offers 2 sets of voltage and frequency protection limit values. The user is allowed to
switch between these 2 sets anytime.
This feature is especially usefull in dual voltage or frequency gensets for easy switching
between 2 operating conditions.
The switching to the second set of limit values is performed by applying signal to the SPARE-1
digital input.
In order to assign this functionality to the SPARE-1 input, the program parameter P_092
Secondary Volt/Freq should be set to 1.
Below parameters are available for second voltage-frequency selection:
Mains Low Voltage Limit
Mains High Voltage Limit
Mains Low Frequency Limit
Mains High Frequency Limit
Genset Low Voltage Shutdown Limit
Genset Low Voltage Warning Limit
Genset High Voltage Warning Limit
Genset High Voltage Shutdown Limit
Genset Low Frequency Shutdown Limit
Genset Low Frequency Warning Limit
Genset High Frequency Warning Limit
Genset High Frequency Shutdown Limit
Genset Low RPM Shutdown Limit
Genset Low RPM Warning Limit
Genset High RPM Warning Limit
Genset High RPM Shutdown Limit
If the unit is used in a single phase electrical network, it is advised t set the Single Phase
Enable program parameter in CONTROLLER CONFIGURATION group to 1.
When Single Phase Enable is set to 1, then the unit will measure electrical parameters only
on phases L1 of genset and mains.
Voltage and overcurrent checks will be performed on phases L1 only.
Phases L2 and L3 parameters, as well as phase-to-phase voltages are removed from
display screens.
The unit is capable to be programmed to ask for a password when AUTO or RUN mode is
selected.
The password is adjusted with parameter P_115. If the password is set to zero, then the unit
will not ask for password.
When the unit asks for password, enter the password with ▼and ▲ buttons, then
acknowledge with MENU button.
- 24 -
DKG-307 User Manual
V-42 (24.05.2013)
(ONLY CANBUS VERSIONS)
The unit offers a special J1939 port in order to communicate with electronic engines controlled
by an ECU (electronic control unit).
The J1939 port consists of 2 terminals which are J1939+ and J1939-. The connection
between the unit and the engine should be made with either a twisted cable pair or a coaxial cable. If a
coaxial cable is used, the external conductor should be grounded at one end only.
The 120 ohms termination resistor is included inside the unit. Please do not connect external
resistor.
The J1939 port is activated by setting the program parameter J1939 Enable to 1. The J1939
Engine Type parameter should be set accordingly. The list of available engines is given at the
programming section. Please contact DATAKOM for the most current list of engines.
If the J1939 port is enabled then the oil pressure, coolant temperature and the engine rpm
information are picked up from the ECU unit. Other available measurements have no effect on engine
operation. In total, the unit is capable of receiving 21 parameters from the J1939.
The J1939 measurements are also available for Modbus operation. Please check chapter 8 for
more details.
When the fuel output is active, if no information is received from the ECU during last 3
seconds, then the unit will give a ECU FAIL alarm and stop the engine. This feature prevents
uncontrolled engine operation.
The fault conditions of an electronic engine are considered by the unit as warnings and do
not cause engine stop. The engine is supposed protected by the ECU which will stop it when
necessary.
The electronic engine fault codes are displayed within the alarm list table in text, together
with their SPN-FMI codes. A maximum of 8 fault codes can be displayed.
The complete list of fault codes is given in the engine manufacturer’s user manual.
- 25 -
DKG-307 User Manual
V-42 (24.05.2013)
Below is a basic list of fault conditions (x denotes any FMI)
SPN
94
FMI
x
98
x
100
x
102
x
105
x
107
x
108
110
x
x
111
x
164
x
168
172
x
x
174
x
175
x
190
x
228
234
620
629
651
652
653
654
655
656
657
657
678
723
1108
1111
2000
x
x
x
x
x
x
x
x
x
x
x
x
x
x
x
x
x
DESCRIPTION
Fuel filter restriction
Fuel pressure sensor fail
Low oil level
High oil level
Oil level sensor fail
Low oil pressure
Oil pressure sensor fail
High boost pressure
Turbo outlet pressure sensor fail
Intake manifold temp high
Intake manifold temp sensor fail
Air filter restriction
Air filter sensor fail
Athmospheric pressure sensor fail
High coolant temperature
Coolant temperature sensor fail
Low coolant level
Coolant level sensor fail
High injector activation pressure
Injector activation pressure sensor fail
Battery voltage failure
High inlet air temperature
High inlet manifold air temperature
Inlet manifold air temperature sensor fail
High fuel temperature
Fuel temperature sensor fail
High oil temperature
Oil temperature sensor fail
Overspeed
Speed sensor loss of signal
Speed sensor mechanical failure
Timing calibration required
Incorrect ecm software
ECU internal +5V fail
ECU hardware fail
Injector cylinder #1 fault
Injector cylinder #2 fault
Injector cylinder #3 fault
Injector cylinder #4 fault
Injector cylinder #5 fault
Injector cylinder #6 fault
Injector cylinder #7 fault
Injector cylinder #8 fault
ECU internal power supply fail
Secondary engine speed sensor fail
Critical override enabled
Check configuration parameters
ECU failure
- 26 -
DKG-307 User Manual
V-42 (24.05.2013)
Below is a basic list of FMI codes.
Please be aware that these codes may differ slightly depending on the engine brand and
model.
FMI
0
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
19
20
21
22
23
24
25
26
27
28
29
30
31
DESCRIPTION
Value too high” Valid data, but above the normal working range
“Value too low” Valid data, but below the normal working range
“Faulty data” Intermittent or faulty data or
Short circuit to battery voltage, injector high voltage side
“Electrical fault” Abnormally high voltage or short circuit to battery
voltage, injector low voltage side
“Electrical fault” Abnormally low voltage or short circuit to battery
negative, injector low voltage or high voltage side
“Electrical fault” Abnormally low current or open circuit
“Electrical fault” Abnormally high current or short circuit to battery
negative
“Mechanical fault” Faulty response from mechanical system
“Mechanical or electrical fault” Abnormal frequency
“Communication fault” Abnormal updating rate or
Open circuit in injector circuit
“Mechanical or electrical fault” Abnormally large variations
“Unknown fault” Unidentified fault
“Component fault” Faulty unit or component
“Faulty calibration” Calibration values outside the limits
“Unknown fault” Special instructions
Data valid but above normal operating range - least severe level
Data valid but above normal operating range - moderately severe level
Data valid but below normal operating range - least severe level
Data valid but below normal operating range - moderately severe level
Received network data in error
not used (reserved)
not used (reserved)
not used (reserved)
not used (reserved)
not used (reserved)
not used (reserved)
not used (reserved)
not used (reserved)
not used (reserved)
not used (reserved)
not used (reserved)
Condition exist
- 27 -
DKG-307 User Manual
V-42 (24.05.2013)
The unit offers the possibility of MODBUS communication via its RS232 serial port.
The connection to the MODBUS master may be done in 3 ways:
1) RS232 connection using directly the RS232 port provided.
2) RS422/485 connection using external RS422/485 converter.
3) Modem connection using external modem.
The MODBUS mode is activated by assigning a controller address to the unit using MODBUS
Address program parameter. The possible address range is 1 to 144. Setting the address to 0 will
disable the MODBUS mode and allow communication under RAINBOW protocol.
The MODBUS properties of the unit are:
-Data transfer mode: RTU
-Serial data: 9600 bps, 8 bit data, no parity, 1 bit stop
-Supported functions:
-Function 3 (Read multiple registers)
-Function 6 (Write single register)
Detailed description about the MODBUS protocol is found in the document “Modicon Modbus
Protocol Reference Guide”. The web address is: www.modbus.org/docs/PI_MBUS_300.pdf
Below is a limited shortlist of readable registers. For the detailed Modbus Application
Manual and a complete list of registers please contact DATAKOM.
ADDRESS
(hex)
0000
0001
0002
0003
0004
0005
0006
0007
0008
000C
000D
000E
000F
0010
0011
0012
0013
0016-0017
R/
W
R
R
R
R
R
R
R
R
R
R
R
R
R
R
R
R
R
R
DATA
SIZE
16bit
16bit
16bit
16bit
16bit
16bit
16bit
16bit
16bit
16bit
16bit
16bit
16bit
16bit
16bit
16bit
16bit
32bit
COEFFICIENT
0018
R
8bit
x100
002A
002B
002C
002D
002F
003D
R
R
R
R
R
R
16bit
16bit
16bit
16bit
16bit
8bit
x1
x10
x1
x1
x10
x1
x1
x1
x1
x1
x1
x1
x1
x1
x1
x1
x1
x1
x1
x1
x10
x10
x256
DESCRIPTION
Mains Phase L1 voltage
Mains Phase L2 voltage
Mains Phase L3 voltage
Genset Phase L1 voltage
Genset Phase L2 voltage
Genset Phase L3 voltage
Genset Phase L1 current
Genset Phase L2 current
Genset Phase L3 current
Mains Phase L12 voltage
Mains Phase L23 voltage
Mains Phase L31 voltage
Genset Phase L12 voltage
Genset Phase L23 voltage
Genset Phase L31 voltage
Mains frequency
Genset frequency
Genset active power: this 24 bit signed register holds
the genset active power multiplied by 256. Least
significant 16 bits are in the register 0016h. Most
significant 8 bits are in the LSB of the register 0017h.
Power factor multiplied by 100 (signed byte). Negative
values indicate a capacitive power factor.
Engine speed (rpm)
Oil pressure in bars.
Coolant temperature in degrees C.
Fuel level as %
Battery voltage
Operating mode
bit_3: manual mode
bit_4: auto mode
bit_5: off mode
bit_6: test mode
bit_7: load test mode
- 28 -
DKG-307 User Manual
V-42 (24.05.2013)
In most applications, the genset is requested to operate only in working hours. Thanks to the
weekly program feature unwanted operation of the genset may be prohibited.
The unit has one programmable turn-on/turn-off time pairs for each day of week. These
programmable parameters allow the genset to operate automatically only in allowed time limits.
The weekly operation schedule is only active in AUTO mode. In other modes it will not affect
the genset operation.
In AUTO mode, if the operation of the genset is disabled by the weekly schedule, then the
AUTO led will flash (instead of a steady on state).
Each turn-on/turn-off time is defined in 10 minute steps.
Unused programs should be set to 24:00.
An example setup may be as follows:
Monday
Monday
Tuesday
Tuesday
Wednesday
Wednesday
Thursday
Thursday
Friday
Friday
Saturday
Saturday
Sunday
Sunday
Turn_on
Turn_off
Turn_on
Turn_off
Turn_on
Turn_off
Turn_on
Turn_off
Turn_on
Turn_off
Turn_on
Turn_off
Turn_on
Turn_off
07:00
18:00
07:00
18:00
07:00
18:00
07:00
18:00
07:00
18:00
07:00
13:00
24:00 (Sunday no turn on time, last operation mode continues)
24:00 (Sunday no turn off time, last operation mode continues)
If the same time is used for turn on and turn off, then it will be considered as a turn-on time.
The unit has a battery backed-up precision real time clock circuit. The real time clock circuit
will continue its operation even in power failures. The real time clock is precisely trimmed using the
Real Time Clock Adjust program parameter. For more details check the programming section.
- 29 -
DKG-307 User Manual
V-42 (24.05.2013)
10. EVENT LOGGING
The unit keeps record of the last 100 events in order to supply information for the service personal.
The genset status information and a comprehensive set of measured values are stored within the
event memory. The events are recorded with a time stamp which comes from the internal real time
clock circuit of the unit.
The events are stored in a circular memory. This means that a new coming event will erase the oldest
recorded event.
Events are kept in a non-volatile memory and are not affected from power failures.
Events are not visible on the device display. They can be downloaded to the computer and saved in
an Excel file.
Event sources are:
-Shutdown alarms, Load dump alarms, Warnings
-Engine crank starts
-Periodic records.
Event record contents are:
Event type (alarms, mode change, periodic, etc…)
Date and time
Genset operating mode (AUTO, MANUAL,OFF,TEST, LOAD TEST)
Genset operation status (mains ok, running, cooldown etc…)
Genset phase voltages L1-L2-L3
Genset phase currents L1-L2-L3
Genset frequency
Genset active power (KW)
Genset power factor
Engine rpm
Oil pressure
Coolant temperature
Fuel level
Battery voltage
Mains phase voltages L1-L2-L3
Mains frequency
Digital input statuses
Charge input status
J1939 VAlues (if applicable)
The unit provides a set of non resettable incremental counters for statistical purposes.
The counters consist on:
-total engine hours
-total genset KWh
-engine hours to service
-time to service
-total engine cranks
-total genset runs
These counters are kept in a non-volatile memory and are not affected from power failures.
- 30 -
DKG-307 User Manual
V-42 (24.05.2013)
12. MAINTENANCE
DO NOT OPEN THE UNIT !
There are NO serviceable parts inside the unit.
Wipe the unit, if necessary with a soft damp cloth. Do not use chemical agents
- 31 -
DKG-307 User Manual
V-42 (24.05.2013)
13. PROGRAMMING
The program mode is used to program timers, operational limits and the configuration of the unit.
To enter the program mode, hold pressed the MENU►button for 5 seconds.
When the program mode is entered, the upper display will show “PRGM” and the mid display
will indicate the program parameter number. The lower display will show the parameter value.
If the PROGRAM LOCK input is tied to GROUND, the program value modification will be
disabled to prevent unauthorized intervention.
It is advised to keep the PROGRAM LOCK input tied to GROUND.
The program mode will not affect the operation of the unit. Thus programs may be modified
anytime, even while the genset is running.
Navigation between program parameters is performed via the MENU►button. Holding the
button pressed will cause the program parameter number to increase faster.
Parameter value may be increased and decreased with ▼and
held pressed, the program value will be increased/decreased faster.
▲buttons. If these keys are
When a program parameter is modified, it is automatically saved in memory.
If MENU►button is pressed, next parameter will be displayed.
Program parameters are kept in a non-volatile memory and are not affected from power
failures.
To exit the program mode press one of the mode selection keys. If no button is pressed during 1
minute the program mode will be cancelled automatically.
Program parameters are organized in 2 groups as low and high levels. Entering the program
mode by pressing the MENU►button will allow access to only low level parameters.
In order to access all parameters please hold OFF and MENU►buttons pressed.
- 32 -
DKG-307 User Manual
V-42 (24.05.2013)
PGM
Parameter Definition
Unit
P_000
Current Transformer
Ratio
A
P_001
Overcurrent Limit
A
P_002
Excess Power Limit
KW
P_003
Mains Voltage Low
Limit
V
P_004
Mains Voltage High
Limit
V
P_005
Mains Frequency Low
Limit
Hz
P_006
Mains Frequency
High Limit
Hz
P_007
Genset Low Voltage
Shutdown Limit
V
P_008
Genset Low Voltage
Warning Limit
V
P_009
Genset High Voltage
Warning Limit
V
P_010
Genset High Voltage
Shutdown Limit
V
P_011
Low Frequency
Shutdown
Hz
P_012
P_013
P_014
P_015
P_016
P_017
Low Frequency
Warning
High Frequency
Warning
High Frequency
Shutdown
Low Battery Voltage
Warning
High Battery Voltage
Warning
Shutdown
Hz
Hz
Hz
V
V
V
Fact.Set Description
This is the rated value of current transformers.
500
All transformers must have the same rating.
The secondary of the transformer will be 5 Amps.
If the current goes above this limit, during the
period defined in Overload Timeout then a
Overcurrent Load Dump alarm will be generated.
0
If this parameter is 0 then Overcurrent check is
disabled.
If the active power goes above this limit, during the
period defined in Overload Timeout then an
Excess Power Load Dump alarm will be
0
generated.
If this parameter is 0 then Excess Power check is
disabled.
If one of the mains phases goes under this limit, it
170
means that the mains are off and it starts the
transfer to the genset in AUTO mode.
If one of the mains phases goes over this limit, it
270
If the mains frequency goes under this limit, it
45
If the mains frequency goes above this limit, it
55
If one of the generator phase voltages goes under
this limit when feeding the load, this will generate a
190
GENSET LOW VOLTAGE shutdown alarm and
the engine will stop.
200
GENSET LOW VOLTAGE warning.
If one of the generator phase voltages goes above
250
GENSET HIGH VOLTAGE warning.
If one of the generator phase voltages goes over
260
GENSET HIGH VOLTAGE alarm and the engine
will stop.
If the genset frequency goes under this limit, a
GENSET LOW SPEED alarm is generated and the
30
engine stops.
35
GENSET LOW SPEED warning is generated.
If the genset frequency goes over this limit, a
54
GENSET HIGH SPEED warning is generated.
GENSET HIGH SPEED alarm is generated and the
55
engine stops.
If the battery voltage falls below this limit, this will
9.0
generate a LOW BATTERY warning.
If the battery voltage goes over this limit, this will
31.0
generate a HIGH BATTERY warning.
generate a HIGH BATTERY shutdown alarm and
33.0
- 33 -
DKG-307 User Manual
PGM
V-42 (24.05.2013)
Unit
P_018
Low Oil Pressure
Warning
bar
P_019
Low Oil Pressure
Shutdown
bar
P_020
High Temperature
Warning
°C
P_021
High Temperature
Shutdown
°C
P_022
Low Fuel Warning
P_023
Low Fuel Shutdown
P_024
High Oil Temperature
Warning
°C
P_025
Shutdown
°C
P_026
Oil Pressure Sender
type
P_027
Coolant Temp.
Sender Type
P_028
Oil Temp. Sender
Type
If the oil pressure measured from the analog input
falls below this limit, this will generate a LOW OIL
1.4
PRESSURE SENDER warning.
1.0
PRESSURE SENDER alarm is generated and the
engine stops.
If the coolant temperature measured from the
95
analog input goes over this limit, this will generate
a HIGH TEMPERATURE SENDER warning.
98
a HIGH TEMPERATURE SENDER alarm and the
engine will stop.
If the fuel level measured from the analog input
falls below this limit, a LOW FUEL LEVEL
20
SENDER warning is generated.
the fuel level measured from the analog input falls
below this limit, a LOW FUEL LEVEL SENDER
10
shutdown alarm is generated and the engine stops.
If the oil temperature measured from the analog
100
input goes over this limit, this will generate a HIGH
OILTEMPERATURE SENDER warning.
120
OIL TEMPERATURE SENDER alarm and the
engine will stop.
This parameter selects the oil pressure sender
type.
0: Non standard sender. The sender
1
This parameter selects the temperature sender
type:
0: The sender characteristics are defined in
1
1: VDO
2: DATCON DAH type
3: DATCON DAL type
type:
1
1: VDO
2: DATCON DAH type
3: DATCON DAL type
- 34 -
DKG-307 User Manual
PGM
V-42 (24.05.2013)
Unit
P_029
Hysteresis Voltage
V
P_030
Engine Heating
Temperature
°C
P_031
Fault Holdoff Timer
sec
P_032
Overload Timeout
sec
P_033
Engine Start Delay
sec
P_034
Preheat Timer
sec
P_035
Choke Timer
sec
P_036
Gas Solenoid Delay
sec
P_037
Crank Timer
sec
P_038
Wait Between Starts
sec
P_039
Idle Speed Timer
sec
P_040
sec
P_041
Mains Waiting Timer
min
P_042
Cooldown Timer
min
This parameter provides the mains and genset
voltage limits with a hysteresis feature in order to
prevent faulty decisions.
For example, when the mains are present, the
8
mains voltage low limit will be used as the
programmed low limit. When the mains fail, the
low limit will be incremented by this value. It is
advised to set this value to 8 volts.
If it is requested that the engine runs without load
until reaching a certain temperature, this
parameter defines the temperature.
0
If the coolant temperature falls below this
parameter, an Engine Low Temperature warning
will occur.
This parameter defines the delay after the engine
12
runs and before the fault monitoring is enabled.
This is the period between the current or active
power go over the limits and OVERCURRENT or
EXCESS POWER Load Dump alarms occur.
This is also the period between the frequency goes
out of the limits and OVERSPEED or
5
UNDERSPEED alarms occur.
This is also the period between the genset voltage
goes out of the limits and HIGH VOLTAGE or LOW
VOLTAGE alarms occur.
This is the time between the mains fails and the
fuel solenoid turns on before starting the genset. It
0
prevents unwanted genset operation in battery
backed-up loads.
This is the time after the fuel solenoid is energized
and before the genset is started. During this
1
period the PREHEAT relay output is energized (if
assigned by Relay Definitions)
This is the control delay of CHOKE output.
The choke output is activated together with the
5
crank output. It is released after this delay or when
engine runs (whichever occurs first).
The gas solenoid of the gas engine will be opened
5
after this delay during cranking.
This is the maximum start period. Starting will be
10
automatically cancelled if the genset fires before
the timer.
This is the waiting period between two start
10
attempts.
When the engine runs, the Idle output relay
0
function will be active during this timer.
This is the period used for engine heating
4
following the program parameter.
This is the time between the mains voltages
0.5
entered within the limits and the generator
contactor is deactivated.
This is the period that the generator runs for cooling
1.0
purpose after the load is transferred to mains.
- 35 -
DKG-307 User Manual
PGM
V-42 (24.05.2013)
Unit
P_043
Genset Contactor
Timer
sec
P_044
Mains Contactor
Timer
sec
P_045
Stop Solenoid Timer
sec
P_046
Number of Starts
P_047
Mains Phase Order
Enable
P_048
Genset Phase Order
Loaddump
P_049
RPM from genset
frequency
P_050
Crank Teeth Count
P_051
Low rpm Shutdown
rpm
P_052
Low rpm Warning
rpm
P_053
High rpm Warning
rpm
P_054
High rpm Shutdown
rpm
P_055
Alarm Relay Timer
sec
P_056
Intermittent Alarm
Relay
P_057
Service Engine Hours
P_058
Service Period
hour
month
This is the period after the mains contactor has
1
been deactivated and before the generator
contactor has been activated.
This is the period after the generator contactor has
1
been deactivated and before the mains contactor
has been activated.
This is the maximum time duration for the engine
to stop. During this period the STOP relay output
is energized (if assigned by Relay Definitions). If
10
the genset has not stopped after this period, a
FAIL TO STOP warning occurs.
3
This is the maximum number of start attempts.
0: mains phase order checking disabled
1: if mains phase order is faulty, then a warning is
0
given and mains contactor deenergized.
0: genset phase order checking disabled
1: if genset phase order is faulty, then a loaddump
0
is generated and the genset stops after cooldown.
This parameter is used in the conversion of the
genset frequency to engine rpm.
1
0: read rpm from the optional MPU input
1: convert frequency to rpm (using crank teeth
count)
This is the number of pulses generated by the
magnetic pickup sensing unit in one turn of the
flywheel.
30
This parameter is also used in the conversion of
the genset frequency to engine rpm. The
frequency in Hz is multiplied with this parameter
during conversion to rpm.
If the engine speed goes under this limit, a GENSET
LOW SPEED alarm is generated and the engine
0
stops.
0
If the engine speed goes over this limit, a GENSET
0
HIGH SPEED alarm is generated and the engine
0
stops.
This is the period during which the ALARM relay
60
is active. If the period is set to 0, this will mean
that the period is unlimited.
0: continuous
0
1: intermittent (turns on and off every second)
The SERVICE REQUEST led indicator will turn on
after this quantity of engine hours from the last
service. If the period is set to ‘0’ no SERVICE
50
REQUEST will be generated depending on engine
hours.
after this amount of time from the last service. If
6
the period is set to ‘0’ no SERVICE REQUEST will
be indicated depending on time.
- 36 -
DKG-307 User Manual
V-42 (24.05.2013)
Following parameters are in “high” priority group.
PGM
Unit
P_059
Reverse power
warning limit
KW
P_060
Reverse power
loaddumpg limit
KW
P_061
P_062
Load Shedding Low
Limit
Load Shedding High
Limit
KW
KW
P_063
Fuel Pump Low Limit
P_064
P_065
Fan turn-on temp
°C
P_066
Fan turn-off temp
°C
P_067
Engine Heating
Method
P_068
Crank Cut Frequency
P_069
Crank Stop with Oil
Pressure
P_070
Crank Stop with
Charge
P_071
Charge Alternator
Shutdown
P_072
Line-to-Line Voltages
P_073
Oil Pressure in psi
P_074
Temperature in °F
Hz
If the genset power is negative and goes above
this limit then a REVERSE POWER warning will
0
be generated.
this limit then a REVERSE POWER loaddump will
0
be generated.
If the genset power goes below this limit then the
0
load shedding relay will be deactivated.
If the genset power goes above this limit then the
0
load shedding relay will be activated.
20
falls below this level, then the FUEL PUMP
function will become active.
80
goes above this level, then the FUEL PUMP
function will become passive.
If the coolant temp is above this limit then the fan
90
relay function will become active.
If the coolant temp is below this limit then the fan
80
relay function will become inactive.
This parameter defines the engine heating
method. The genset will not take the load before
engine heating is completed.
0: engine is heated during Engine Heating Timer.
0
1: engine is heated until the coolant temperature
reaches the Engine Heating Temperature and at
least during the Engine Heating Timer.
When the genset frequency reaches this limit, the
10.0
engine is supposed running and the crank output
will release.
0: no crank stop with oil pressure
1: cranking is stopped when oil presure switch is
0
open or the oil pressure measured is above
shutdown limit.
0: no crank stop with charge input
1: cranking is stopped when the charge alternator
0
voltage is established.
0: The charge input generates CHARGE FAIL
warning, and does not stop the engine.
0
1: The charge input generates CHARGE FAIL
alarm, and stops the engine.
0: Display Line to Neutral voltages as default
0
1: Display Line to Line voltages as default
0: oil pressure display in bars
0
1: oil pressure display in psi
0: temperature display in degrees C
0
1: temperature display in degrees F
- 37 -
DKG-307 User Manual
PGM
V-42 (24.05.2013)
Unit
P_075
Single phase Enable
P_076
Emergency Backup
Operation
P_077
Modem Enable
P_078
SMS Enable
P_079
MODBUS Address
P_080
SMS on Mains
Change
P_081
Fuel Consumption per
Hour
P_082
Real Time Clock
Adjust
P_083
Remote Start Enable
P_084
Simulate Mains
Enable
P_085
Delayed Simulate
Mains
P_086
hours
0: 3-phase system
0
1: Single phase system
0: In TEST mode, the load will not be transferred
to the genset even if the mains fail.
0
1: In TEST mode, the load will be transferred to
the genset if the mains fail.
0: No modem connection, the serial port is
0
connected to PC
1: Modem connected.
0: SMS not enabled
0
1: SMS enabled
0: RAINBOW communication protocol.
1-144: MODBUS communication. This parameter
0
is also the MODBUS controller address of the unit.
This parameter controls SMS sending when mains
voltages status is changed. No warning is
0
generated.
0: no SMS when mains failed or restored
1: SMS sent when mains failed or restored
This parameter is the threshold for sending FUEL
THEFT and FUELLING sms messages.
If this parameter is set to 0, then no Fuel Theft and
0
Fuelling sms messages will be sent.
If SMS is required, set this parameter to a value
above the hourly fuel consumption of the genset.
This parameter trims precisely the real time clock
circuit.
Values from 0 to 63 speed up the clock with
117
0.25sec/day steps.
Values from 127 to 64 slow down the clock with
0.25sec/day steps.
0: no Remote Start signal
0
1: SPARE-2 input is Remote Start signal
0: no Simulate Mains signal
0
1: SPARE-2 input is Simulate Mains signal
0: The SPARE-2 input has normal function
1: The SPARE-2 input has delayed simulate
0
mains function. See chapter 6.8 for more info.
Delayed Simulate Mains Operation: max
genset running time after Simulate Mains signal
disappears.
0
Dual Genset Systems: flashing relay toggle
timer. Please contact DATAKOM for dual genset
mutual stanby operation.
- 38 -
DKG-307 User Manual
PGM
V-42 (24.05.2013)
Unit
P_087
Exercise Day and
Time
P_088
Exercise Duration
min
P_089
Exercise Off/On Load
P_090
Exercise Period
P_091
Language Selection
P_092
Secondary Volt/Freq
P_093
Engine Control Only
This parameter defines the start day and hour of
the exerciser.
Values higher or equal to 168 mean that the
exerciser is off.
The exercise may be selected to start at the
beginning of the any hour of the week. The
parameter value is the hour count of the start time.
Examples:
0 = exercise starts at Monday 00:00
8 = exercise starts at Monday 08:00
168
24 = exercise starts at Tuesday 00:00
167 = exercise starts at Sunday 23:00
168 = exerciser off
If a daily exercise is selected, then the day
information is don’t care and the exercise will be
performed every day regardless of the day
selection.
If the monthly exerciser is selected, then the
exercise will be performed during the first 7 days
of each month at the programmed day and hour.
This parameter defines the exercise duration and
10
programmed in 10 minute steps up to 24 hours.
0: Exercise at TEST mode
0
1: Exercise at LOAD TEST mode
0: exercise every day (the exercise will be
selection of Exercise Dat and Time parameter).
1: exercise once per week
1
2: exercise once per month (the exercise will be
performed during the first 7 days of each month at
the programmed day and hour).
This is the language used in SMS messages.
0: english
1: turkish
0
2: french
3: russian
0: Use primary voltage/frequency limits
1: When signal is applied to the SPARE-1 input,
0
use secondary voltage/frequency limits
0: Genset control
0
1: Engine control (no alternator
- 39 -
DKG-307 User Manual
V-42 (24.05.2013)
Below parameters are applicable to J1939 enabled
versions only.
PGM
Unit
P_094
J1939 Enable
P_095
J1939 Engine Type
P_096
J1939 Speed Adjust
P_097
VOLVO Speed
Toggle
0: The J1939 port is inoperative.
1: The analog measurements (oil, temp, rpm) are
0
picked_up from the ECU. If the ECU communication
is lost, then the engine will be stopped.
00: GENERIC ENGINE TYPE
16: CUMMINS CM850
32: DETROIT DIESEL
48: DEUTZ Generic
49: DEUTZ EMR2
50: DEUTZ EMR3
64: JOHN DEERE
80: PERKINS
81: PERKINS ADEM 3
82: PERKINS ADEM 1.3
96: VOLVO (with CIU unit)
97: VOLVO EMS2
98: VOLVO EDC4
112: CATERPILLAR ADEM II/III
0
128: SCANIA S6
129: SCANIA Single Speed
130: SCANIA All Speed
144: IVECO
160: MTU MDEC 302
161: MTU MDEC 201
162: MTU MDEC 303
163: MTU MDEC 304
164: MTU MDEC 505
176: BOSCH Generic
177: BOSCH EDC 731
178: BOSCH EDC 9.3
Other values: Reserved. Do not use.
This parameter adjusts the speed of an ECU
50
controlled engine by +/- 8%.
This program parameter is not stored, but only used
in order to activate the primary or secondary speed
selection operation of a Volvo EMS-II engine control
unit.
0: Initiate the primary speed select operation
1: Initiate the secondary speed select operation
- 40 -
DKG-307 User Manual
PGM
V-42 (24.05.2013)
Unit
P_098
2nd Overcurrent Limit
A
P_099
2nd Mains Voltage
Low Limit
V
P_100
2nd Mains Voltage
High Limit
V
P_101
2nd Mains Frequency
Low Limit
Hz
P_102
2nd Mains Frequency
High Limit
Hz
P_103
2nd Genset Low
Voltage Shutdown
Limit
V
P_104
2nd Genset Low
V
P_105
2nd Genset High
V
P_106
2nd Genset High
Voltage Shutdown
Limit
V
P_107
2nd Low Frequency
Shutdown
Hz
P_108
2nd Low Frequency
Warning
Hz
P_109
2nd High Frequency
Warning
Hz
P_110
2nd High Frequency
Shutdown
Hz
When secondary volt/freq limits are active:
0
disabled.
84
136
55
65
90
94
130
136
will stop.
40
engine stops.
45
65
69
engine stops.
- 41 -
DKG-307 User Manual
PGM
V-42 (24.05.2013)
Unit
P_111
2nd Low rpm
Shutdown
rpm
P_112
2nd Low rpm Warning
rpm
P_113
2nd High rpm Warning
rpm
P_114
2nd High rpm
Shutdown
rpm
P_115
Engine Run
Password
0
stops.
0
0
0
stops.
Applicable only to the DKG-317 model:
If this parameter is set to a value other than zero,
0
then when AUTO or RUN mode is selected, the unit
will ask for this password.
Date - Time
P_116
P_117
P_118
P_119
P_120
P_121
Date
Month
Year
Hours
Minutes
Seconds
Current day of the month.
Current month.
Last two digits of the current year.
Current hour of the day.
Current minute of the hour.
Current second of the minute.
Weekly Schedule Programs
PGM
P_122
P_123
P_124
P_125
P_126
P_127
P_128
P_129
P_130
P_131
P_132
P_133
P_134
P_135
Monday Turn_on
Monday Turn_off
Tuesday Turn_on
Tuesday Turn_off
Wednesday Turn_on
Wednesday Turn_off
Thursday Turn_on
Thursday Turn_off
Friday Turn_on
Friday Turn_off
Saturday Turn_on
Saturday Turn_off
Sunday Turn_on
Sunday Turn_off
Unit
hh:mm
hh:mm
hh:mm
hh:mm
hh:mm
hh:mm
hh:mm
hh:mm
hh:mm
hh:mm
hh:mm
hh:mm
hh:mm
hh:mm
Factory
Set
24:00
24:00
24:00
24:00
24:00
24:00
24:00
24:00
24:00
24:00
24:00
24:00
24:00
24:00
Description
Please review chapter 9 for a detailed
description of weekly programming schedule
operation.
- 42 -
DKG-307 User Manual
V-42 (24.05.2013)
Oil Pressure Sender Characteristics
PGM
P_136
P_137
P_138
P_139
P_140
P_141
P_142
P_143
P_144
P_145
P_146
P_147
Oil Pressure Sender Ohms -1
Oil Pressure Value -1
Oil Pressure Sender Ohms -2
Oil Pressure Value -2
Oil Pressure Sender Ohms -3
Oil Pressure Value -3
Oil Pressure Sender Ohms -4
Oil Pressure Value -4
Oil Pressure Sender Ohms -5
Oil Pressure Value -5
Oil Pressure Sender Ohms -6
Oil Pressure Value -6
Unit Factory Set
10
ohm
0.0
bar
52
ohm
2.0
bar
90
ohm
4.0
bar
140
ohm
7.0
bar
156
ohm
8.0
bar
184
ohm
10.0
bar
Description
Oil Pressure Sender point 1, ohm value
Oil Pressure Sender point 1, bar value
Oil Pressure Sender point 2, ohm value
Oil Pressure Sender point 2, bar value
Oil Pressure Sender point 3, ohm value
Oil Pressure Sender point 3, bar value
Oil Pressure Sender point 4, ohm value
Oil Pressure Sender point 4, bar value
Oil Pressure Sender point 5, ohm value
Oil Pressure Sender point 5, bar value
Oil Pressure Sender point 6, ohm value
Oil Pressure Sender point 6, bar value
Coolant Temperatıre Sender Characteristics
PGM
P_148
P_149
P_150
P_151
P_152
P_153
P_154
P_155
P_156
P_157
P_158
P_159
Temperature Sender Ohms -1
Temperature Value -1
Temperature Sender Ohms -2
Temperature Value -2
Temperature Sender Ohms -3
Temperature Value -3
Temperature Sender Ohms -4
Temperature Value -4
Temperature Sender Ohms -5
Temperature Value -5
Temperature Sender Ohms -6
Temperature Value -6
Unit Factory Set
38
ohm
100
°C
51
ohm
90
°C
134
ohm
60
°C
322
ohm
39
°C
650
ohm
20
°C
1630
ohm
02
°C
Description
Temperature Sender point 1, ohm value
Temperature Sender point 1, °C value
Temperature Sender point 2, ohm value
Temperature Sender point 2, °C value
Temperature Sender point 3, ohm value
Temperature Sender point 3, °C value
Temperature Sender point 4, ohm value
Temperature Sender point 4, °C value
Temperature Sender point 5, ohm value
Temperature Sender point 5, °C value
Temperature Sender point 6, ohm value
Temperature Sender point 6, °C value
Fuel Level Sender Characteristics
PGM
P_160
P_161
P_162
P_163
P_164
P_165
P_166
P_167
P_168
P_169
P_170
P_171
Fuel Level Sender Ohms -1
Fuel Level Value -1
Fuel Level Sender Ohms -2
Fuel Level Value -2
Fuel Level Sender Ohms -3
Fuel Level Value -3
Fuel Level Sender Ohms -4
Fuel Level Value -4
Fuel Level Sender Ohms -5
Fuel Level Value -5
Fuel Level Sender Ohms -6
Fuel Level Value -6
Unit Factory Set
4
ohm
0
31
ohm
25
67
ohm
50
110
ohm
75
180
ohm
100
1000
ohm
100
Description
Fuel Level Sender point 1, ohm value
Fuel Level Sender point 1, % value
Fuel Level Sender point 2, ohm value
Fuel Level Sender point 2, % value
Fuel Level Sender point 3, ohm value
Fuel Level Sender point 3, % value
Fuel Level Sender point 4, ohm value
Fuel Level Sender point 4, % value
Fuel Level Sender point 5, ohm value
Fuel Level Sender point 5, % value
Fuel Level Sender point 6, ohm value
Fuel Level Sender point 6, % value
- 43 -
DKG-307 User Manual
V-42 (24.05.2013)
Program Group: Sender Characteristics (password level-2)
PGM
P_172
P_173
P_174
P_175
P_176
P_177
P_178
P_179
P_180
P_181
P_182
P_183
Oil Temperature Sender Ohms -1
Oil Temperature Value -1
Oil Temperature Sender Ohms -2
Oil Temperature Value -2
Oil Temperature Sender Ohms -3
Oil Temperature Value -3
Oil Temperature Sender Ohms -4
Oil Temperature Value -4
Oil Temperature Sender Ohms -5
Oil Temperature Value -5
Oil Temperature Sender Ohms -6
Oil Temperature Value -6
Unit Fact.Set Description
38
ohm
100
°C
51
ohm
90
°C
134
ohm
60
°C
322
ohm
39
°C
650
ohm
20
°C
1630
ohm
02
°C
Low Oil Pressure Switch Input Configuration
PGM
P_184
Action
P_185
Sampling
P_186
Latching
P_187
Contact type
P_188
Switching
P_189
Unit
Response delay
Fac.Set Description
0: Shutdown (the engine stops immediately)
1: Load Dump (the engine stops after cooldown)
0
2: Warning (the horn relay operates)
3: No operation
0: Always
1: After holdoff timer
1
2: When mains present
0: Non latching
1
1: Latching
0: Normally open
0
1: Normally closed
0: Battery negative
0
1: Battery positive
0: No delay
0
1: Delayed (4sec)
High Temperature Switch Input Configuration
PGM
P_190
Action
P_191
Sampling
P_192
Latching
P_193
Contact type
P_194
Switching
P_195
Response delay
Unit
Fac.Set Description
0
3: No operation
0: Always
1
0: Non latching
1
1: Latching
0: Normally open
0
1: Normally closed
0: Battery negative
0
1: Battery positive
0: No delay
0
1: Delayed (4sec)
- 44 -
DKG-307 User Manual
V-42 (24.05.2013)
Coolant Level Switch Input Configuration
PGM
P_196
Action
P_197
Sampling
P_198
Latching
P_199
Contact type
P_200
Switching
P_201
Unit
Response delay
Fac.Set Description
0
3: No operation
0: Always
0
0: Non latching
1
1: Latching
0: Normally open
0
1: Normally closed
0: Battery negative
0
1: Battery positive
0: No delay
1
1: Delayed (4sec)
Rectifier Fail Input Configuration
PGM
P_202
Action
P_203
Sampling
P_204
Latching
P_205
Contact type
P_206
Switching
P_207
Unit
Response delay
Fac.Set Description
2
3: No operation
0: Always
2
0: Non latching
1
1: Latching
0: Normally open
0
1: Normally closed
0: Battery negative
0
1: Battery positive
0: No delay
0
1: Delayed (4sec)
Emergency Stop Input Configuration
PGM
P_208
Action
P_209
Sampling
P_210
Latching
P_211
Contact type
P_212
Switching
P_213
Response delay
Unit
Fac.Set Description
0
3: No operation
0: Always
0
0: Non latching
0
1: Latching
0: Normally open
0
1: Normally closed
0: Battery negative
0
1: Battery positive
0: No delay
0
1: Delayed (4sec)
- 45 -
DKG-307 User Manual
V-42 (24.05.2013)
Spare–1 Input Input Configuration
PGM
P_214
Action
P_215
Sampling
P_216
Latching
P_217
Contact type
P_218
Switching
P_219
Response delay
Unit Fac.Set Description
2
3: No operation
0: Always
0
0: Non latching
0
1: Latching
0: Normally open
0
1: Normally closed
0: Battery negative
0
1: Battery positive
0: No delay
0
1: Delayed (4sec)
Spare-2 Input Input Configuration
PGM
P_220
Action
P_221
Sampling
P_222
Latching
P_223
Contact type
P_224
Switching
P_225
Response delay
2
3: No operation
0: Always
0
0: Non latching
0
1: Latching
0: Normally open
0
1: Normally closed
0: Battery negative
0
1: Battery positive
0: No delay
0
1: Delayed (4sec)
- 46 -
DKG-307 User Manual
V-42 (24.05.2013)
The parameters below define the functions of relay outputs. The unit has 6 relay outputs. The
fixed function relays are Fuel, Start, Mains Contactor and Generator Contactor. RELAY-1 and RELAY2 have programmable functions, selected from a list.
The relays may be extended up to 22 using Relay Extension Modules.. Other relays are in
the optional Extension Modules.
Program Group: Relay Definitions (password level-2)
PGM
P_226
Relay 01 Definition
3
RELAY-1 function selected from list
P_227
Relay 02 Definition
1
RELAY-2 function selected from list
P_228
Relay 03 Definition
0
RELAY-3 function (expansion module) selected from
list
P_229
Relay 04 Definition
2
RELAY-4 function (expansion module-1) selected
from list
P_230
Relay 05 Definition
4
RELAY-5 function (expansion module-1) selected
from list
P_231
Relay 06 Definition
5
RELAY-6 function (expansion module-1) selected
from list
P_232
Relay 07 Definition
0
RELAY-7 function (expansion module-1) selected
from list
P_233
Relay 08 Definition
2
RELAY-8 function (expansion module-1) selected
from list
P_234
Relay 09 Definition
4
RELAY-9 function (expansion module-1) selected
from list
P_235
Relay 10 Definition
5
RELAY-10 function (expansion module-1) selected
from list
P_236
Relay 11 Definition
0
RELAY-11 function (expansion module-2) selected
from list
P_237
Relay 12 Definition
2
RELAY-12 function (expansion module-2) selected
from list
P_238
Relay 13 Definition
4
RELAY-13 function (expansion module-2) selected
from list
P_239
Relay 14 Definition
5
RELAY-14 function (expansion module-2) selected
from list
P_240
Relay 15 Definition
0
RELAY-15 function (expansion module-2) selected
from list
P_241
Relay 16 Definition
2
RELAY-16 function (expansion module-2) selected
from list
P_242
Relay 17 Definition
4
RELAY-17 function (expansion module-2) selected
from list
P_243
Relay 18 Definition
5
RELAY-18 function (expansion module-2) selected
from list
- 47 -
DKG-307 User Manual
V-42 (24.05.2013)
The function of a programmable relay output may be selected from below list.
00
01
02
03
04
05
06
07
08
09
10
11
12
13
14
15
16
17
18
19
20
21
22
23
24
25
26
27
28
29
30
31
Fuel
Alarm
Start
Stop
Gen. Contactor
Mains Contactor
Choke
Preheat
Shutdown alarm
Shutdown or
load_dump alarm
Shutdown or
load_dump or warning
Automatic ready
Week. on time
Exerciser on
Load_dump alarm
Fuel Main winding
Mains Fail
Block Heater
Service Request
Load Shedding Relay
Flashing Relay
Gas Solenoid
Fuel Pump
Mains Phase Order
Fail
Genset Phase Order
Fail
Idle Speed
Cooler Fan
2nd volt-frequency
Crank 1/2 Selector
32
33
34
35
36
37
38
39
40
41
42
43
44
45
46
47
48
49
50
51
52
53
54
55
56
57
58
59
60
61
62
63
64
65
66
67
68
69
70
71
72
73
74
75
76
77
78
79
Oil switch alarm
Temp switch alarm
Coolant Level switch
alarm
Rectifier alarm
Emerg.Stop alarm
Spare-1 Alarm
Spare-2 Alarm
Oil sender alarm
Temp sender alarm
Low speed alarm
High speed alarm
Low voltage alarm
High voltagealarm
Fail to start alarm
Low fuel sender alarm
High oil temp alarm
High battery voltage
alarm
Charge fail alarm
Oil switch load_dump
Temp switch
load_dump
load_dump
Rectifier load_dump
Emerg.Stop load_dump
Spare-1 load_dump
Spare-2 load_dump
Overcurrent load_dump
Excess power ldd
Reverse power ldd
Genset Phase Order
Fail Loaddump
80
81
82
83
84
85
86
87
88
89
90
91
92
93
94
95
96
97
98
99
100
101
102
103
104
105
106
107
108
109
110
111
112
113
114
115
116
117
118
119
Oil switch warning
Temp switch warn.
warning
Rectifier warning
Emerg Stop warn.
Spare-1 warning
Spare-2 warning
Oil sender warning
Temp sender warn.
Low speed warning
High speed warning
Low temp warning
Fail to stop warning
Low fuel sender
warning
Service request
warning
Mains Phase Order
Fail
Low battery warning
High battery warning
Charge fail warning
Gen Low voltge warn.
Gen High voltge warn.
Reverse Power warn.
High oil temp warn.
- 48 -
DKG-307 User Manual
V-42 (24.05.2013)
14. TROUBLESHOOTING
The genset operates while AC mains are OK or continues to operate after AC mains are OK:
-Check engine body grounding.
-AC mains voltages may be outside programmed limits, measure the phase voltages.
-Check the AC voltage readings by pressing the MENU button.
-Upper and lower limits of the mains voltages may be too tight. Check the parameters Mains Voltage
Low Limit and Mains Voltage High Limit. Standard values are 170/270 volts.
-The hysteresis voltage may be given to excessive. The standard value is 8 volts.
AC voltages or frequency displayed on the unit are not correct:
-Check engine body grounding, it is necessary.
-The error margin of the unit is +/- 3 volts.
-If there are faulty measurements only when the engine is running, there may be a faulty charging
alternator or voltage regulator on the engine. Disconnect the charging alternator connection of the
engine and check if the error is removed.
-If there are faulty measurements only when mains are present, then the battery charger may be
failed. Turn off the rectifier fuse and check again.
Phase-to-Phase AC voltages are not correct although Phase to Neutral voltages are correct:
-Incorrect phase order. Please connect phase voltages in the correct order.
KW and cosΦ readings are faulty although the Amp readings are correct:
-Current transformers are not connected to the correct inputs or some of the CTs are connected with
reverse polarity. Determine the correct connections of each individual CT in order to obtain correct KW
and cosΦ for the related phase, and then connect all CTs.
Short circuit the outputs of unused Current Transformers.
When the AC mains fails the unit energizes the fuel solenoid, but does not start and OIL
PRESSURE EXISTS ! message is displayed:
The unit is not supplied with battery (-) voltage at the oil pressure input.
-Oil pressure switch not connected.
-Oil pressure switch connection wire cut.
-Oil pressure switch faulty.
-Oil pressure switch closes too lately. If oil pressure switch closes, the unit will start. Optionally oil
pressure switch may be replaced.
The engine does not run after the first start attempt, then the unit does not start again and OIL
-The oil pressure switch closes very lately. As the unit senses an oil pressure, it does not start. When
oil pressure switch closes the unit will start. Optionally the oil pressure switch may be replaced.
- 49 -
DKG-307 User Manual
V-42 (24.05.2013)
When the AC mains fails, the engine starts to run but the unit gives START FAIL alarm and
then the engine stops:
-The generator phase voltages are not connected to the unit. Measure the AC voltage between
terminals GEN L1-L2-L3 and Generator Neutral at the rear of the unit while the engine is running. A
fuse protecting the generator phases may be failed. A misconnection may be occurred. If everything
is OK, turn all the fuses off, and then turn all the fuses on, starting from the DC supply fuse. Then test
the unit again.
The unit is late to remove engine cranking:
-The generator voltage rises lately. Also the generator remnant voltage is below 20 volts. The unit
removes starting with the generator frequency, and needs at least 20 volts to measure the frequency.
If this situation is to be avoided, the only solution is to add an auxiliary relay. The coil of the relay will
be between BATTERY (-) and charging alternator D+ terminal. The normally closed contact of the
relay will be connected serially to the unit's START output. So the starting will also be removed when
the D+ pulls to battery positive.
The unit is inoperative:
Measure the DC-supply voltage between terminals 19 and 22 at the rear of the unit. If OK, turn all the
fuses off, then turn all the fuses on, starting from the DC supply fuse. Then test the unit again.
Programming mode can not be entered:
The program lock input disables programming mode entry. Disconnect the program lock input from
battery negative before modification. Do not forget to make this connection again to prevent
unauthorized program modifications.
Some program parameters are skipped:
These parameters are reserved for factory setting and cannot be modified.
AUTO led flashes and the genset does not run when mains fail:
The unit is in Weekly Schedule OFF time. Please check date and time setting of the unit. Please
check also Weekly Schedule program parameters.
- 50 -
DKG-307 User Manual
V-42 (24.05.2013)
15. DECLARATION OF CONFORMITY
The unit conforms to the EU directives
-2006/95/EC (low voltage)
-2004/108/EC (electro-magnetic compatibility)
Norms of reference:
EN 61010 (safety requirements)
EN 61326 (EMC requirements)
The CE mark indicates that this product complies with the European requirements for safety,
health environmental and customer protection.
UL / CSA Conformity:
certificate # 20110527-E314374
UL 508, Edition 17
UL 2200, 1st Edition.
UL 840 Edition 3
CSA C22.2 NO. 14 - Edition 10
- 51 -
DKG-307 User Manual
V-42 (24.05.2013)
16. TECHNICAL SPECIFICATIONS
Alternator voltage: 0 to 300 V-AC Phase to Neutral (0 to 520 V-AC Phase to Phase)
Alternator frequency: 0-100 Hz.
Mains voltage: 0 to 300 V-AC Phase to Neutral (0 to 520 V-AC Phase to Phase)
Mains frequency: 0-100 Hz.
DC Supply range: 9.0 VDC to 33.0 VDC
Cranking dropouts: survives 0 V for 100ms
Typical stand-by current consumption: 100 mADC.
Maximum current consumption: 250 mADC.
Generator/mains contactor outputs: 16 A @ 250 VAC.
DC outputs: 10A @ 28 VDC. relay outputs.
Charge alternator excitation: min 2W.
Magnetic pickup input:: 0.5 – 30 V-AC.
Magnetic pickup frequency: 10 KHz max.
Current inputs: from current transformers, .../5A. Max load 0.7VA per phase.
Digital inputs: input voltage 0 - 30 VDC. Internally connected to battery positive via 47’000 ohm resistor.
Analog inputs: Resistor input 0 to 5000 ohms connected to the battery negative. Sources 5 mA when
closed to battery negative.
Measurement category: CAT II
Air category: Pollution degree II
Communication port: RS-232. 9600 bauds, no parity, 1 stop bit.
Operating temperature range: -40°C to +70°C (-40 ºF to +158 ºF)
Storage temperature range: -55°C to +80°C (-67ºF to +176ºF)
Maximum humidity: 95%, non-condensing
Dimensions: 172x134x46mm (WxHxD)
Panel Cut-out dimensions: 151 x 111mm minimum.
Weight: 340 g (approx.)
Case material: High temperature, self extinguishing ABS/PC (UL94-V0)
IP protection: IP65 from front panel, IP30 from the rear
- 52 -
DKG-307 User Manual
V-42 (24.05.2013)
17. CONNECTION DIAGRAMS
- 53 -
DKG-307 User Manual
V-42 (24.05.2013)
DATAKOM Electronics Ltd.
Tel: +90-216-466 84 60 Fax: +90-216-364 65 65 e-mail: datakom@datakom.com.tr http: www.datakom.com.tr
- 54 -
